pv wire and ferrule question

wrench 87

New Member
Joined
Feb 19, 2022
Messages
58
Location
Seekonk, Ma
I was just looking for opinions on using temco 10 awg pv wire it is stranded but course,should you use a crimp ferrule going in to the dc breaker pros and cons.
 
It depends on what type of terminal is on the breaker. And how fine the strands are in the conductor.
If the terminal is a clamping type. No ferrule is needed.
If it's a set scew type of terminal. The screw can damage fine strands as it's tightened. And a ferrule will protect the strands from damage.
 
If it's a set scew type of terminal. The screw can damage fine strands as it's tightened. And a ferrule will protect the strands from damage.

@AntronX @rhino @timselectric @Skypower

So anytime you have a set screw type of terminal, you should always use a ferrule? This is completely new information for me and means I need to redo some things in my system. Which brand or type of ferrules do you recommend?

Can you also please address this comment which has been upvoted by a few people claiming that ferrules shouldn't be used on some set screw type terminals? Are these guys wrong, or there's exceptions, or...?
 
Last edited:
@AntronX @rhino @timselectric @Skypower

So anytime you have a set screw type of terminal, you should always use a ferrule? This is completely new information for me and means I need to redo some things in my system. Which brand or type of ferrules do you recommend?

Can you also please address this comment which has been upvoted by a few people claiming that ferrules shouldn't be used on some set screw type terminals? Are these guys wrong, or there's exceptions, or...?


see this.

 
This is a clamp style breaker(clones?). The serrated "clamp" tightens the wire when the screw is tightened. The screw type would just be the screw pushing the wire .
View attachment 214704
I have this style breaker and it is designed for stranded wires. The serrated surface isn’t raised so it does little to help retain the wire. After tightening 10 AWG thhn, I found that I could wiggle the wire out after using reasonable amount of tightening torque without distorting the case. TEMCo 10 AWG solar wire wasn’t as bad as for poor retaining, probably due to the finer strands. For both types of wire I found out that stripping the wire twice as long as normal and folding it in half then inserting into the terminal keeps it in place. You will also need to follow up on tightening a few times as the strands settle. I’ve had them a couple years now with no problems just be sure that the screws are snugged up! Remember that the screws are live and you don’t get dead.
I tried ferrules in these and they got hot and not sure why but ferrules here are not the answer for me.
IMG_1071.jpeg
 
For both types of wire I found out that stripping the wire twice as long as normal and folding it in half then inserting into the terminal keeps it in place
I like this idea. Makes sense that it would work better. I'm going to try it when I connect to grid using the "clamp type" on my inverter.
 
I have this style breaker and it is designed for stranded wires. The serrated surface isn’t raised so it does little to help retain the wire. After tightening 10 AWG thhn, I found that I could wiggle the wire out after using reasonable amount of tightening torque without distorting the case. TEMCo 10 AWG solar wire wasn’t as bad as for poor retaining, probably due to the finer strands. For both types of wire I found out that stripping the wire twice as long as normal and folding it in half then inserting into the terminal keeps it in place. You will also need to follow up on tightening a few times as the strands settle. I’ve had them a couple years now with no problems just be sure that the screws are snugged up! Remember that the screws are live and you don’t get dead.
I tried ferrules in these and they got hot and not sure why but ferrules here are not the answer for me.
View attachment 214733

Ferrules get hot if they are not the right size for the wire and aren't full when crimped. Or if the walls are to thin or to thick. Or if you use the wrong shape crimper. For your picture it would need the 4 sided crimper.


Only needed it the wire is fine stranded. For the solid did you use a torque screwdriver and get it tight enough?


Three squeeks is not the same as a torque wrench of screwdriver
 
I have this style breaker and it is designed for stranded wires. The serrated surface isn’t raised so it does little to help retain the wire. After tightening 10 AWG thhn, I found that I could wiggle the wire out after using reasonable amount of tightening torque without distorting the case. TEMCo 10 AWG solar wire wasn’t as bad as for poor retaining, probably due to the finer strands. For both types of wire I found out that stripping the wire twice as long as normal and folding it in half then inserting into the terminal keeps it in place. You will also need to follow up on tightening a few times as the strands settle. I’ve had them a couple years now with no problems just be sure that the screws are snugged up! Remember that the screws are live and you don’t get dead.
I tried ferrules in these and they got hot and not sure why but ferrules here are not the answer for me.
View attachment 214733
I have a similar breaker and 10awg PV wire.
Although the strands are pretty thick, I preferred to use ferrules. No problems so far.
 