for dark start, you could add a 12v car battery or other connected to a 120v inverter to supply a 120vac source to the inverter, unless the AC source has to be synch'd to the grid ...that is down???
Many inverters won't start from 120v input, they need 240v. specifically offgrid type inverters. (Though, some do, to be fair).
So this *may* work for some inverters. You'd want to test it, however.
But yes, there are a ton of ways to work around the dark start issue. The specific point I was trying to make is.. "dark start" implies there is no grid available. So any "dark start" plan that involves connecting to the grid in some way, isn't actually a dark start plan.
Not sure if I mentioned it in this thread or not, but.. my panels are connected to DC charge controllers. The "rapid shutdown" transmitter is powered from 12-24v dc. so, in my case.. in my case, I can take the transmitter to one of the follwing 12v sources
Primary option: powered by the 12v output of the inverter. If it's still up and running (not really a dark start)
Backups (actual dark start):
#1) Solar powered gate openers (I have 2, each uses 2 12v batteries)
#2) my portable ham radio setup (solar powered, and AGM batteries)
#3) 3 different vehicles with 12v sources
So in my case, I'd take the RSD transmitter, connect it to any of those sources, and the arrays would all wake up and start charging the batteries. When sufficient charge, inverter can start.