Goin'Solar
New Member
I ordered this battery on Monday and received it on Thursday. Super-fast shipping from Rich Solar... BUT - I open the box and turned on the battery via the breaker and... nothing. Tried connecting it to my MPP Solar 3048LV-MK and still nothing. Tested the output voltage and I'm only getting 6.7 volts at the terminals. Called Rich Solar Thursday afternoon and spoke with their customer service rep. She referred me to their tech who wasn't available so I left a message. Never got a return call. On Friday I called again and she gave me the "direct line" to the service rep. I called and left a message and, again never got a call back.
Via some R*ddit posts and Y*uT*be videos, I was able to get the thing to turn on by sticking a pin in the "Reset" hole, however it's still not working right. So now that I can see the BMS screen, I can see that the readings are wonky. Additionally, the red "ALM" light is on.
Pressing the "Menu" key brings me to
Analog info >>
PackV: 35.76 V
Im: 0.00 A
Cell Voltage>>
Cell01: 1995 mV
Cell02: 0 mV
Cell03: 0 mV
Cell04: 2139 mV
Cell05: 3296 mV
Cell06: 3294 mV
Cell07: 3294 mV
Cell08: 3294 mV
Cell09: 3294 mV
Cell10: 3295 mV
Cell11: 3295 mV
Cell12: 3294 mV
Cell13: 2610 mV
Cell14: 0 mV
Cell15: 2654 mV
Cell16: -- mV
CellCapacity>>
SOC: 49.29%
FCC: 100.00 OAH
Rm: 49.2AH
CC: 1
BMS Status>>
--Status: Failure
>>Record>>
SCP: 1
O/UTP: 0
OCP: 0
UVP: 4
OVP: 3
>>BMS Status>>
UV: Y
UVP: Y
OC: N
OCP: N
SCP: N
--Failure: Y
I'm not sure what all these readings mean since there is no manual that came with the battery (nor is there one available online) but to me, this doesn't look good at all. BMS Failure, mismatched cell voltages and several cells reporting zero. I've read that Rich Solar is a reputable company, but I would think they could at least get back to a new customer within a couple of days on a DOA new product. Does anyone have any experience with this company and/or know what I might try to get this $1500 paperweight running running?
**UPDATE**
I heard back from Rich Solar this morning (8/28/23). I had emailed them a link to this post. Apparently, they read it and will be sending me a return label and granting a full refund.
I would like to thank Al from Rich Solar for being very nice and easy to deal with.
Via some R*ddit posts and Y*uT*be videos, I was able to get the thing to turn on by sticking a pin in the "Reset" hole, however it's still not working right. So now that I can see the BMS screen, I can see that the readings are wonky. Additionally, the red "ALM" light is on.
Pressing the "Menu" key brings me to
Analog info >>
PackV: 35.76 V
Im: 0.00 A
Cell Voltage>>
Cell01: 1995 mV
Cell02: 0 mV
Cell03: 0 mV
Cell04: 2139 mV
Cell05: 3296 mV
Cell06: 3294 mV
Cell07: 3294 mV
Cell08: 3294 mV
Cell09: 3294 mV
Cell10: 3295 mV
Cell11: 3295 mV
Cell12: 3294 mV
Cell13: 2610 mV
Cell14: 0 mV
Cell15: 2654 mV
Cell16: -- mV
CellCapacity>>
SOC: 49.29%
FCC: 100.00 OAH
Rm: 49.2AH
CC: 1
BMS Status>>
--Status: Failure
>>Record>>
SCP: 1
O/UTP: 0
OCP: 0
UVP: 4
OVP: 3
>>BMS Status>>
UV: Y
UVP: Y
OC: N
OCP: N
SCP: N
--Failure: Y
I'm not sure what all these readings mean since there is no manual that came with the battery (nor is there one available online) but to me, this doesn't look good at all. BMS Failure, mismatched cell voltages and several cells reporting zero. I've read that Rich Solar is a reputable company, but I would think they could at least get back to a new customer within a couple of days on a DOA new product. Does anyone have any experience with this company and/or know what I might try to get this $1500 paperweight running running?
**UPDATE**
I heard back from Rich Solar this morning (8/28/23). I had emailed them a link to this post. Apparently, they read it and will be sending me a return label and granting a full refund.
I would like to thank Al from Rich Solar for being very nice and easy to deal with.