That might be an easy solution to my issue. Would I have to add the same size battery? Or could I add a smaller 100AH Lithium battery?
The great thing with LFP is you can have different sized battery packs without huge problems. I run 3x 280AH, 2x 174AH & 1x105AH in one bank. Yeah I know what a weird mix, but the 105 is going to the Toolshed so temporarily it's in my main bank. They are all running with JKBMS and the EVE 280's & 105's all came from
https://szluyuan.en.alibaba.com/ as did the BMS's which are cheaper there. They carry JK, JBD (Overkill) and others like Seplos, Pace etc.
The GOTCHA !
(of course there has to be some, right)
Everything works totally peachy when all the packs are within the working voltage ranges. 11.6-23.2-46.4 to 13.6-27.2-54.4 which is from 2.900-3.400 Volts per cell.
-- When
Charging everything stays nicely together voltage wise right through to 100% SOC (Assuming 100% is 3.400Vpc).
- As lower AH Packs fill and their "Amps Taken" drops below EndAmps/TailCurrent they go into rest/balancing mode taking only minimal voltage while balancing out internally. The larger packs continue to take Amperage until they also get just below their EndAmp/TailCurrent value. When ALL are "saturated" and not taking any amperage, the packs balance out between themselves to the Set Float Voltage.
-- When
Discharging, they all stay in-line and discharge Proportianetly relative to their capacity, IE a bank with a 100AH & 280AH with a 30A demand will show as 10A being drawn for the 100AH & 20A from the 280AH which is perfectly normal. This will continue this way until your cells reach the bottom of the working Voltage Range at which point you will start to see deviations between the packs. The lower power packs will discharge less while the larger packs pickup the load, (as expected). BUT the larger packs will also attempt to Backcharge the smaller packs and this will be seen with the BMS as the amperage transfer occurs. At this point there is LOSS of energy as the transfer from one pack to another loses some along the way.
!! DUE TO THIS ISSUE noted above, one must NEVER set BMS Low Volt Disconnect too low otherwise you may not be able to restart a disconnected BMS to take charge if too low. If things have gone too far and the bigger packs back-charged and still dropped below LVD they likely will NOT recover to reconnection point. It is best to set LVD (Low Volt Disconnect) to 2.700 or better yet 2.800 and set the Recovery Point to 2.750 or 2.850. It is also better to keep the reconnect threshold @ 0.050 volts which is well within the recoverable range post demand.
Calculate EndAmps/TailCurrent:
This is a simple calculation that determines at what point the cells are full "saturated". This is the point where Bulk/Absorb Charging has to change to Float (Variable Current which tops off battery packs while servicing ongoing demand as available).
100AH Battery X 0.05 = 5A, or, 280Ah X 0.05 = 14A.
With a Bank of Battery Packs, you calculate what the EndAmps are for all the packs, If for example you have a 100AH & 280AH packs in Parallel, then the EndAmps for the 100AH is 5A and the 280AH is 14A, divide the difference and use that (14A - 5A = 4.5A. 5A (lowest pack) + 4.5A (the difference divided in half) added to lowest pack for 9.5A Bank EndAmps. *Number of Battery Packs in Parallel makes no difference".
BTW Cash Saving Tip: (adds up fast too)
IF buying cells from Vendor A check to see if they also carry the BMS' etc that you need. Most often they DO and if you get them to package it all together, you save on the MIN Cost "per box" + Min Weight charges it adds up fast, especially with different vendors shipping stuff. The Couriers charge "per box" minimum fee, box size & weight fees & number of packages rate... AND ALSO depending on What Country being shipped to (Like the USA) there is a new additional "Consumption Tax" which just came into effect (May 2023).
Hope it helps, Good Luck