On my older inverter, which was a Xantrex, it was old school and required a manual reset when I overloaded it. Maybe your will at least have an overload light on it?
I did not see anything in the logs. Everything looked fine. Nothing red or greater than 0 for logged alerts.Conservatively, the microwave is going to draw 135 amps on the DC side (1380 watts / 12 / .85 = 135) based on your Killawatt meter. The label says 13 amps AC and using that we get 152 amps DC, Which should be well within the capability of your two batteries.
It would help to know what is shutting down. Was it the inverter or one of the batteries? You'll have to look at the logs. If even one of those batteries shuts down then you lose everything on the DC side because the other battery will also shut down due to overload from trying to carry all those amps by itself.
Check all your connections. A poor connection can show great voltage, but when put under load you'll get very few amps and the voltage will drop.
For comparison, my microwave is very similar.
View attachment 158324
My inverter is a Multiplus 12/3000 (effectively 2400 watts). I've had no problems running my microwave on high for five minutes. Running continuously doesn't sound like your problem, it's the startup surge. Before blaming your inverter, we need to know if your batteries are shutting down.
I have a 24V system for the inverter and it will pull over 50A as it turns the mag on/off.I’ve included what is noted on the MW for the power rating in the one attachment. (All I recall is it’s noted to be a 2002 model and LG but apparently rebranded as Dometic.) Not sure what the wiring is for the MW because it was pre wired as well as unsure what the wiring was that they used to pre wire it for the solar. It’s a 2003 Arctic Fox 990. The wires for the batteries and the inverter are using 2/0 copper wires. The batteries were at least 97% when we attempted to the MW yesterday when it kept cutting out… yet it’s odd as I’m pretty sure we had it work once before earlier this trip. Also just tried the MW again in the driveway and it’s still shutting off after 2-3 seconds and was at 98%….I just took a picture of the microwave specs inside the MW and also included a picture from the manual I found online as attached. (When I put the KillaWatt display meter on tonight, it read 1380 watts and 13 amps and didn’t seem to catch any sort of surge at startup.) ps- Sadly I was not able to get any good shots of the setup at this time.
Unfortunately I really can’t get any good pictures as it’s pretty tight in there ….the wiring is located in the cupboard that also houses the sink plumbing (and yes, I know, electronics and water is a bad combination… but it was really the only place there was available for it as we’re in a truck camper and there’s very limited available real estate available…)
Just need to know how to determine if it’s the bms or the inverter that’s causing it to cut out at startup.
The other odd thing is that it seems to run the toaster oven fine off the inverter while it’s parked in the driveway here and no external additional power.On my older inverter, which was a Xantrex, it was old school and required a manual reset when I overloaded it. Maybe your will at least have an overload light on it?
AFAIK, we had nothing else running simultaneously … also, now that we’re home, and are trying to troubleshoot this issue, we turned everything we knew was possibly a draw off … the fridge totally off, the fans are off, the UV system for the water off, the led lights off, the phone chargers were unplugged, etc… There was nothing else we could find that could have been actively simultaneously drawing anything from the LiFePO4 batteries. And odd.y enough the 1000w toaster oven also seems to do fine plugged into it. It’s looking like possibly its a bms issue. The one battery that’s at 100% is showing as locked on the bms app, so maybe that’s also stopping the bms on that battery from discharging as well versus just locking it out from charging? I guess maybe I’ll have to call the battery company and see if that’s possibly what’s happening. They also have new BMSs available that are rated for 200a now, so maybe we will have to pursue buying 2 new BMSs and upgrade from what’s currently installed on them. If only one battery and bms is actively “available“ - due to the lock on the one that’s at 100% so that it doesn’t overcharge the battery- maybe that’s actually what’s playing into this issue and causing the trouble of it’s over the 125a limit of the single bms…i don’t think the inverter needs to be reset as other things seem to work off of it currently, the microwave is just not one of them.I’ve included what is noted on the MW for the power rating in the one attachment. (All I recall is it’s noted to be a 2002 model and LG but apparently rebranded as Dometic.) Not sure what the wiring is for the MW because it was pre wired as well as unsure what the wiring was that they used to pre wire it for the solar. It’s a 2003 Arctic Fox 990. The wires for the batteries and the inverter are using 2/0 copper wires. The batteries were at least 97% when we attempted to the MW yesterday when it kept cutting out… yet it’s odd as I’m pretty sure we had it work once before earlier this trip. Also just tried the MW again in the driveway and it’s still shutting off after 2-3 seconds and was at 98%….I just took a picture of the microwave specs inside the MW and also included a picture from the manual I found online as attached. (When I put the KillaWatt display meter on tonight, it read 1380 watts and 13 amps and didn’t seem to catch any sort of surge at startup.) ps- Sadly I was not able to get any good shots of the setup at this time.
Cool! Thank you! Somehow I didn’t see this reply earlier, but I will share it with hubs in the morning and see what we can find out!Put a meter on battery #1 and turn on the microwave. If the meter shows no voltage when the microwave shuts down, then you know that battery stopped discharging. If the meter still shows voltage then do the same test with the other battery.
You may see that both batteries shut down and you'll have to figure out which one is shutting down first. It may happen so fast that you can't figure it out with just a simple voltmeter. Either way, if you see the batteries shut down then you know it isn't likely to be the inverter.
Well not sure what being out of phase looks like, but I would not be surprised if this MW is “out of phase“….Even with using the generator, I seem to have to ”prime” the MW by first turning on the toaster oven momentarily and then it will finally power on the MW display… so this MW has been sort of quirky for a while now actually, and have just had to endure it… thanks for your replySo your microwave lists a consumption of 1500W. So let's call it a 1500W microwave, even though it only outputs 1000W.
1500w/12.8v/0.85 (inverter inefficiency) = 137A.
That 137A is the running power, but the startup surge would be more.
Let's say startup surge is 4500W. Your 3000W inverter is supposed to be able to handle twice that, for 6000W. But for how long? Not sure Renogy lists for how many seconds (or milliseconds is probably the likelihood) it can handle 6000W. Or how many milliseconds it can handle 4500W for your microwave startup surge.
But it might be your startup surge amps is more than the BMS's can handle. 4500w/12.8v/0.85= 413A
Again, your BMS's, the two together in parallel, can handle up to 250A continuously, but how much can they handle for surges and for how many milliseconds, before the BMS shuts down?
Perhaps someone can help you narrow down if it's the inverter or the BMS konking out, but my bet it's one of those.
I have also heard that microwaves can be especially difficult for some inverters to start because 1) surge is actually 5-6x, not just 3x (clamp meter could measure this, but you'd want a beefy one) and/or 2) something to do with microwaves being out of phase (this is where my electrical knowledge plummets so I'm parroting from poor memory) with the inverter (not sure what the fix is).
And odd.y enough the 1000w toaster oven also seems to do fine plugged into it.
Hmph, that’s odd. No idea why the mw display shows only if the toaster oven is on. Again, maybe it’s that phase thing I mentioned. Hopefully someone knowledgeable about the quirks of a microwave on an inverter will chime in.Well not sure what being out of phase looks like, but I would not be surprised if this MW is “out of phase“….Even with using the generator, I seem to have to ”prime” the MW by first turning on the toaster oven momentarily and then it will finally power on the MW display… so this MW has been sort of quirky for a while now actually, and have just had to endure it… thanks for your reply
Hmph, that’s odd. No idea why the mw display shows only if the toaster oven is on. Again, maybe it’s that phase thing I mentioned. Hopefully someone knowledgeable about the quirks of a microwave on an inverter will chime in.
I’ve also read that some people have tried a different microwave and the second one worked whereas the first one didn’t. Might be worth trying if you have an extra one around.
Your wording implies that microwaves of any type might cook from the inside out. They do not. Microwaves of any type heat the surface of the food, and the interior is heated by conduction from the warm/hot surface.
Matter is not invisible to microwaves. Microwaves excite the first water molecules they meet. They do not jump over/past water molecules to get to others. The primary cooking benefit of inverter microwaves is the ability to heat at a true reduced power so the surface heating rate is more comparable to the rate of conduction heating of the interior.
I’ve also read that certain Renogy inverters don’t play nice with certain BMS’s. I don’t recall what brand of lifepo4 batteries that OP is using. Iirc, the story I read was with a Renogy 1000W inverter and an SOK (or was it Chins?) battery. Others had reported a similar quirk.Agreed, odd. It's starting to sound like the microwave itself is the problem.
When I was a boy and microwaves first came out, my granny used to always say , “ these things are the work of the devil, these things ain’t right” …Hi all,
I built a 280AH battery using a 120amp Overkill BMS. I've got a 2200 watt pure sine inverter and I tried to run my rv microwave and it shut down the bms. Looking at the specs on the microwave, it takes a 1500 watt as input, 1000 watt as output. So that makes sense... 1500w / 12v = 125 amps. I guess the bms should shutdown. So I then tried to run the microwave on low power thinking that that would reduce the input amperage. Nope, still shutdown the bms. Strange, unless the input stays the full 1500 watt amount regardless of the output.
So, I am now considering swapping out to a smaller 1000 watt microwave in the hopes that it wouldn't shutdown the bms. 1000w / 12v = 84 amps. Do you think that would work?
Thanks so much!
How many watts is your microwave?
According to a quick google search, a 900W microwave can draw as many as 2700W to start up. This means it can draw about 250A from your battery for 1-2 seconds. A decent BMS should be able to handle a short burst like that, and even then your 2x125A BMS is good for 250A, continuous...in theory. Also your wiring can make a huge difference. If your wiring between the batteries or between the inverter and battery bank is too small, you WILL have voltage drop and the result is the microwave will try to draw even more amps to make up for it, resulting in more voltage drop...it can become a vicious cycle.
So as @HRTKD suggested, a photo of your wiring would help people give you more specific advice.
I’ve also read that some people have tried a different microwave and the second one worked whereas the first one didn’t. Might be worth trying if you have an extra one around.
That's interesting. We also had a 1200 Watt Panasonic inverter microwave and found that a Honda 2000 could run it on 50% but not on any setting higher than 50% which indicates that load drawn does depend on power setting. Our Panasonic may have been newer than yours, we went to a 600 Watt unit because it fits our kitchen better.
My understanding is that modern inverter microwaves run the magnetron on lower current for lower power settings whereas standard microwaves achieve lower power by pulsing the magnetron on and off to get a lower duty cycle delivered to the food.
too bad there is no such thing as a "devil".When I was a boy and microwaves first came out, my granny used to always say , “ these things are the work of the devil, these things ain’t right” …
your a very considerate and gracious individual… thank you for your input… have a nice life..too bad there is no such thing as a "devil".
Wonder what she would have said about solar panels, electric cars, going to Mars, curing many types of cancer and so many other diseases? Things simply were not better in the "good ol' days" and the human brain's memory is incredibly flawed and inaccurate.
Yea, we were healthier… and other stuff… good call.Any chance the cancer we're (not) curing today, and other diseases, weren't so prevalent in the good old days?
( 's advocate here)