That is what Will points out, the sticker still show 5000 ES, the user manual is shown as 5000 ES.
Yeah caught it later as I caught up...what a cluster F. Updated my post to ignore the question.
That is what Will points out, the sticker still show 5000 ES, the user manual is shown as 5000 ES.
SS needs to at the very least put the sticker on the unit showing what you bought, if you have two of them side, one from SS and one from other vendor, how can you tell which one is the US model? They do not even have the manual for the 5000 US.We bought "ES" version per Signature Solar, it is even on the receipts. That is not jumping to conclusions that is being given incorrect information straight from the manufacturer we bought them from. They should figure out what they are selling.
All of my paperwork/stickets from SS show 5000 ES. No where on my invoice, stickers, manual, does it say USHe should also show us his user manual, see if it says SPF-5000 US or not.
You can only by U.S model from Signature Solar
I am one of the noobs that did research on one set of products(Victron Quattro European), then thought he knew enough and applied it to another set of products(5000se). I am using 3 5000se and 1 Victron Autotransformer. This is an off-grid setup. so I am clear on #1... For #2, The Victron AT is wired directly into the Panel as L1 L2 and Neutral. Are you saying that the AT could fail in a way that still passed L1 and L2 through but not the neutral? #3 The Autotransformer has a breaker built into it, so if it trips it wont pass on any of the legs or neutral.That's a good educational video, that should scare the hell out of most people using this setup.
Lessons for those that don't take the 25 mins to watch all of Ian's video or understand what his trying to tell you (I think he did a good job of explaining this).
1. Autotransformers should NOT be used in systems that connect to the grid "OFF-GRID Use ONLY"
2. If your autotransformer quits functioning for any reason, half the crap in your house is probably going to get fried with 240 volts. (IE breaker trips to it, thermal shutdown, bad wiring, or it simply fails)
3. These 240v non-split phase inverters used with autotransformers probably are NOT a good idea. Yes they work, but the potential for disaster is one breaker trip or autotransformer failure away.
If you already have this setup and can't afford to get a proper inverter, I'd recommend at a minimum:
1. DO NOT put a breaker on neutral legs. This is given, but I had to say it.
2. Make sure the breakers hooked to the L1 L2 of autotransformer are large enough to handle full load on either side.
3. Put the inverter OUTPUT on a breaker and Install a breaker trip bar across the 240v inverter output breaker and both legs of autotransformer breakers. That way if the autotransformer was to trip a breaker, the OUTPUT from your inverter will trip at same time. The goal here is you want the inverter 240v output to be killed if any one of the legs off the autotransformer was to fail or be shutoff.
BTW, this autotransformer issue is not specific to Growatt inverters. The discussion of the bounded grounding screw in the Growatt 5000ES is a separate but related safety concern.
Are you saying that the AT could fail in a way that still passed L1 and L2 through but not the neutral? #3 The Autotransformer has a breaker built into it, so if it trips it wont pass on any of the legs or neutral.
Any suggestion on a good high voltage MPPT? Preferably one that allows to be define battery voltage much higher than 48V? I can't find any stand alone MPPTs on the market ATM. Everything that is high power is integrated into the inverter and the inverters that are high power all have serious limitations too unless 240 only.Just add another or multiple SCC's. You don't have to run all PV thru the inverter MPPT.
That isn't true. UL 1310 isn't required. UL 294 still applies as does NEC standards on high voltage lines both because of the 240VAC and because the inverter boosts 48VDC to 340VDC to supply the inverter to get 240VAC out without a transformer. And it does so with PWM which makes it pulsed DC which is regulated.Not if you are off grid, UL is not a requirement
I have to say, after watching these videos, and even looking at the units that do split phase, it really seems to me that AC passthrough is a bad idea.Thanks Ian.
I hope some of these naysayers finally understand what they are dealing with.
Any suggestion on a good high voltage MPPT? Preferably one that allows to be define battery voltage much higher than 48V? I can't find any stand alone MPPTs on the market ATM. Everything that is high power is integrated into the inverter and the inverters that are high power all have serious limitations too unless 240 only.
Define high voltage. 250V max works well, let's take #8 wire, 200 feet of distance with 4 to 6 conductors in conduit. 3% allowable voltage drop. You can run 19 amps and load voltage would be 194V.Any suggestion on a good high voltage MPPT? Preferably one that allows to be define battery voltage much higher than 48V? I can't find any stand alone MPPTs on the market ATM. Everything that is high power is integrated into the inverter and the inverters that are high power all have serious limitations too unless 240 only.
I have 600W panels. I have 8 in series (and because of location I can' just do 4S2P). So I need 450V. My design had 4 strings of these which fit in the Growatt profile for wattage.Define high voltage. 250V max works well, let's take #8 wire, 200 feet of distance with 4 to 6 conductors in conduit. 3% allowable voltage drop. You can run 19 amps and load voltage would be 194V.
While you think the higher 450VDC would be advantageous, you have to remember the inverter has a max wattage rating. A balance needs to be found between amps/volts where wattage remains within limits. It doesn't work to have 450VDC but can only carry 10 amps or less.
Many are using this MPPT. https://watts247.com/product/sc48120/
Note that it will take 250VDC now, the older models were 150VDC. Contact Ian for more information and tell him what your PV array will be.
Let's get the specs on the panels.I have 600W panels. I have 8 in series (and because of location I can' just do 4S2P). So I need 450V. My design had 4 strings of these which fit in the Growatt profile for wattage.
I would love nothing more than to find separate MPPTs that will handle this and then inverters that can be paralleled that have nothing to do with anything else and then one or more separate AC/DC chargers....
Let's get the specs on the panels.
Maybe, but one of the main reasons people buy the 5000ES is due to the high PV voltage input. This discussion in the thread is relevant as some like John don't see alternatives. If he wishes to start another thread and provide a link here, I'm all for moving the discussion. That way members can be aware of all aspects.
Maybe, but one of the main reasons people buy the 5000ES is due to the high PV voltage input. This discussion in the thread is relevant as some like John don't see alternatives. If he wishes to start another thread and provide a link here, I'm all for moving the discussion. That way members can be aware of all aspects.
YouSolar makes a system similar to that that is stackable, but is is not relatively inexpensive DIY.I have to say, after watching these videos, and even looking at the units that do split phase, it really seems to me that AC passthrough is a bad idea.
The better solution in my mind is to rectify the AC to 340VDC using a ideal rectifier (4 fets pulsed which can also apply PFC) which would generate a 0.5% loss, and then feed that into the SPWM inverter.
I.e. you have the following:
If you did this, you'd be VASTLY more efficient and need VASTLY less inverter power which would save a TON on the cost. (i.e. half/full bridges are always VASTLY cheaper and more efficient to build so even if you do need to convert voltages with DC, it's always cheaper than the copper in a transformer to do it purely AC and more efficient and easier than SPWM inverters.
- AC/DC mains input using a push/pull or Resonant LLC with transformer ideally that is isolated and UL listed. This outputs 340VDC to a internal DC bus. (about 95% or so efficient)
- Battery to DC Bus that boosts using a full bridge design at 98% efficiency whatever your battery voltage to 340VDC, which is required for the inverter anyhow. (this design is symmetrical, which is different than what is in there now which is forward only)
- MPPT that boost/buck as the second stage to the 340VDC bus internally. I.e. you use a half bridge to MPPT with shift and read, and then whatever the output of those maximized watts are, you buck/boost to 340VDC. This would actually be significantly more efficient with high voltage strings than MPPT to 48VDC AND once it's at 340VDC if you're running off of solar there is no further conversion and any excess after the inverter is taken care of will go out to the battery using #2.
- Dual 120VAC outputs capable of taking 100% of the wattage from the internal DC bus as needed to either leg. (and international markets would just be 240VAC doing the same).
- Output 340VDC (you can hack heat pumps and anything else that advertises "DC Inverter" to bypass the rectifier (or use the rectifier harmlessly) and feed this in without having to have huge inverters and save yourself a TON of in efficiency. Same with hot water heaters),
- Output 120VDC (ELV) for things like high dryers etc. (The great problem children of design, but ELV is unregulated up to 120VDC with less than 5% ripple)
- Output 48VDC for USB C 240V plugs. (I'd expect virtually all devices in the next 5 years like TVs etc. to only come with a USB C input because then they don't need UL certification at all, just FCC and any wall wart will work. If you switch the wall to be coming from 48VDC anyhow with USBC ports then you don't need the inefficient wall wart, the inverter nor the rectification. USB C will output 3.3, 5, 9, 12, 18, 20, 24, 28, 36, and 48VDC so you have everything that anything else DC would need so everything with a wall wart would be covered and work.
- Build an on wall DC/DC cart charger for CCS Type 2 that boosts/bucks the 340VDC to whatever the car DC voltage request is at 98+% efficiency thus eliminating the entire need for inverter and then rectification just to charge a car making it 15-25% more efficient which is a big deal on solar off grid.
This is a FET design in a pulsed environment so using GanFETS (600-900VDC max) for most of the design, and SICFets for the MPPT (1800VDC max) works really well and isn't very expensive because the pulsed continuous load rating on these FETs is in the 100s of amps per FET on a 6MM copper board trace.
Honestly thinking about designing one of these as a modular design in a rack... The only part that gets expensive is the AC/DC mains input because of the UL and FCC certification to do it right. Given ENNOID-BMS, this becomes super compelling in design because we can easily scale our batteries to higher voltage with this design and reach better efficiencies on the bus over time as we can afford more batteries, while minimizing inverter power required.