Greetings,
I just ran across this forum today, and hope someone can provide feedback. Attached is a diagram of how I thought I should do this, I'm open to suggestions. In summary, I plan(ed) to swing most of my house load over to 3 new sub panels by moving the wire and breakers. The 3 panels would be "house critical", "house non-critical", "barns". These would be main lug panels feed by 3 transfer switches which switch L1-N-L2 lines. One feed would be from a breaker in the original house panel, the other feed from the output of a Growatt autotransformer. The autotransformer would have 2P 20A breaker between it and the SPF5000ES. The output of the transformer would connect to the 3 transfer switches through an over/under voltage breaker. The 5000ES AC input L&N would be connected to another breaker in the original house panel, to allow for battery top off and bypass as needed. In the house panel, earth ground is bonded to Neutral, it would not be bonded in the sub panels. Earth ground would also be connected to 5000ES and the autotransformer case. Btw, the 5000ES is the US model. I'm thinking, per reading many of the forum posts, this will be ok. as the Neutral in the sub panel is always switched along with the L1/L2 depending on the chosen source. Except, I'm think the earth ground for the 5000ES and autotransformer need to go to a separate grounding rod since the ground and neutral are bonded at the main house panel. Thanks in advance to your thoughts!!
Don't install a second ground rod.
Everything in the system should get its ground from the main panel.
The transfer switches need a 4th pole. This is used to bond the neutral to ground.
"Next comes the tricky part "
In bypass mode, this creates a ground loop. And possible current flowing on the ground conductor.
The best solution for this is to add a relay to disconnect the neutral/ ground bond, and connect a bypass neutral, when the inverter feed breaker is turned on.
And, keep this breaker off when not needed.
So.......
Your neutral/ ground bonding (green 12 gauge) wire and bypass neutral (white appropriatly sized) wire, would go to the relay. (Which would choose which is feed to the transfer switches 4th pole) from the relay, run a white appropriately sized wire to the transfer switches. (4th pole)
Then connect (with an appropriately sized white wire) the output of the 4th pole to the neutral output.
The purpose of this is to provide a neutral from the main panel in bypass mode. And provide a neutral/ ground bond when not in bypass mode.
The last remaining issue is that when in bypass mode, the auto transformer is put in parallel with the grid split-phase transformer.
This is why you should keep the breaker that feeds the inverter off, when not needed.
Hopefully, I made this easy to understand.