Why? taking only L1 and L2 from grid is like use the L1 and L2 on the inverter, in others words there will be no unbalance.That's a major issue for bypass mode.
All of the unbalanced load is going to be on the ground conductor.
Why? taking only L1 and L2 from grid is like use the L1 and L2 on the inverter, in others words there will be no unbalance.That's a major issue for bypass mode.
All of the unbalanced load is going to be on the ground conductor.
(Well there is if there is an unbalance on the 2 legs of 120V created by the auto-transformer, but that's literally why you have the auto-transformer, to balance that out. So as long as you have excess over max unbalance, it is designed to handle it, and if you don't, then you're going to blow up all of your 120V stuff if the breaker on it pops, which we knew. That's why you overside your auto-transformer and by virtue of how electricity works, you'll only experience loss of having a second one hooked up if it's actually in active use. Otherwise it's balanced and thus no electricity flowing through it.Why? taking only L1 and L2 from grid is like use the L1 and L2 on the inverter, in others words there will be no unbalance.
You don't need do that if you connect the inverter directly to the autotransformer, if the breaker pops it will cut the inverter and the autotransformer at the same time...(Well there is if there is an unbalance on the 2 legs of 120V created by the auto-transformer, but that's literally why you have the auto-transformer, to balance that out. So as long as you have excess over max unbalance, it is designed to handle it, and if you don't, then you're going to blow up all of your 120V stuff if the breaker on it pops, which we knew. That's why you overside your auto-transformer and by virtue of how electricity works, you'll only experience loss of having a second one hooked up if it's actually in active use. Otherwise it's balanced and thus no electricity flowing through it.
Yup, that's for the new one and that also implies that you have one auto-transformer per inverter which I don't, because I have a max 5000W imbalance (measured with extensive testing) on the 120V yet I routinely use 27kW of power while charging our car and running our heat pump and the dryer on and the dishwasher and hot water running.You don't need do that if you connect the inverter directly to the autotransformer, if the breaker pops it will cut the inverter and the autotransformer at the same time...
The second autotransformer don't need to be connected in that way...Yup, that's for the new one and that also implies that you have one auto-transformer per inverter which I don't, because I have a max 5000W imbalance (measured with extensive testing) on the 120V yet I routinely use 27kW of power while charging our car and running our heat pump and the dryer on and the dishwasher and hot water running.
So I have 6 inverters with 6 strings of solar, and 2 auto-transformers, of which one of them virtually never has any amperage on it at all. (I've yet to ever drive more than 5.1kW of total 120V and that was just in testing, normally it's under 1.5kW)
If I was to do it again, I'd use EG4s or switch to one of the new 96V inverter/solar charge controllers that do native split phase, but I don't have that kind of money, so I've just made sure I have enough capacity at the cost of a slight power wastage in all circumstances.
The first one is a new one. It's in series with the inverter. The second one is installed with a breaker in the panel and a neutral back to the neutral bus bar. Is there a better way?The second autotransformer don't need to be connected in that way...
You've yet to give a scientific answer as to why we're wrong. Please do enlighten us. As an electrical engineer (i.e. my knowledge comes from a full understanding of the physics, not just a US Code book and the wrote memorization of an electrician), I love to be educated whenever possible.The two of you are welcome to do whatever you choose in your own home.
But please don't recommend it to others.
People come here to learn how to do it properly and safely.
The two of you are welcome to do whatever you choose in your own home.
But please don't recommend it to others.
People come here to learn how to do it properly and safely.
That's exactly the way i connect it.The first one is a new one. It's in series with the inverter. The second one is installed with a breaker in the panel and a neutral back to the neutral bus bar. Is there a better way?
Again, your assertion that, if the neutral from the grid is not connected and there is no ground to the transformer, there will be an imbalance on your ground is wrong. It's very easy to test and I have and the physics doesn't add up either. You literally can't get an imbalance on L1 to L2 (or visa-versa) because any imbalance is literally like putting a resistor in a circuit. This is basic Ohm's law stuff. And if there is an imbalance for any strange reason because of bonding the panel while not connecting the grid's natural, it's going to find the shortest path to source, which because of the bonding, it's the ground wire directly from the panel to the earth. So you MIGHT in some strange case get energy on the ground wire, but it won't ever hit a circuit in your house, because NONE of those paths is the shortest path to anywhere unless you disconnect your earth and if you do that, you've by definition disconnected the bonding and have other problems. (literally every single 120V flyback converter and similar just won't work as a small example)Just read this thread. We have already hashed out everything.
Electrical Engineer? You should be able to figure it out.
Ignore the code?
You are talking about an ungrounded system. Which in battery mode is what you would have in your scenario. But in bypass mode you can't create an ungrounded system while being fed from a grounded system, if using an autotransformer. The source is the grids transformer, which is a grounded system.Again, your assertion that, if the neutral from the grid is not connected and there is no ground to the transformer, there will be an imbalance on your ground is wrong. It's very easy to test and I have and the physics doesn't add up either. You literally can't get an imbalance on L1 to L2 (or visa-versa) because any imbalance is literally like putting a resistor in a circuit. This is basic Ohm's law stuff. And if there is an imbalance for any strange reason because of bonding the panel while not connecting the grid's natural, it's going to find the shortest path to source, which because of the bonding, it's the ground wire directly from the panel to the earth. So you MIGHT in some strange case get energy on the ground wire, but it won't ever hit a circuit in your house, because NONE of those paths is the shortest path to anywhere unless you disconnect your earth and if you do that, you've by definition disconnected the bonding and have other problems. (literally every single 120V flyback converter and similar just won't work as a small example)
And the very scenario you claim is an issue? Telsa power points actually do a direct test and have special functionality for exactly that case, and won't run if you actually have the problem you claim. Which is why Will Prowse had to hack his floating ground pack to charge his Tesla, which of course didn't go well as you'll recall. I have a Tesla power point. Guess what? It has no problem with how it's wired. So physics, an amp meter, and Tesla engineers all agree with me.
But do tell, what scenario would this occur? Because ALL of the back story in this thread that I've found has the grid's neutral hooked up and bonded to the auto-transformer neutral which will absolutely cause a disaster and then people created convoluted approaches to fix when the solution was always: Don't hook up grid neutral to anything and always derive your neutral like any other transformer from the auto-transformer even when getting powered from the grid.
That’s incorrect. L1/L2 are not grounded or bonded to ground anywhere in the North American power system other than your house. The ground on a transformer on the pole is connected to the case and used to create a dead short that breaks the bar breaker on the pole with the transformer in the case of a power to ground event.You are talking about an ungrounded system. Which in battery mode is what you would have in your scenario. But in bypass mode you can't create an ungrounded system while being fed from a grounded system, if using an autotransformer. The source is the grids transformer, which is a grounded system.
This would be possible with an isolation transformer. Because of the separation between primary and secondary. But the L1 and L2 being carried through the autotransformer are already part of a grounded system.
And I might add you’re creating the risk of a short if the neutral does become unbalanced on either side and carries power because when you’re not connected to the grid you just put 240v through a 120v circuit best case and if they’re out of phase, you just created a complete cluster because of the harmonics you created from two power sources out of phase on the same wire. Why? Because the neutral from the grid that’s also indirectly connected to other houses on the same transformer can be carrying power at the phase of the grid and your auto transformer is carrying the unbalanced between the two phases at the phase of your inverters that aren’t synced to the grid. (Growatts do not sync, they hard transfer with a momentary disconnect which is why they’re not grid tie).You are wrong. Only if you connect the neutrals (from grid and the autotransformers) is the only way that they are in the same grounded system.
?. Still haven’t heard any evidence of your claims. At all anywhere. And yes I’ve read essentially all of this thread.You're not going to get it. Your understanding of the US electrical system is too far gone.
I'm just wasting my time here.
I wish you good luck in life.
You've yet to give a scientific answer as to why we're wrong. Please do enlighten us. As an electrical engineer (i.e. my knowledge comes from a full understanding of the physics, not just a US Code book and the wrote memorization of an electrician), I love to be educated whenever possible.
(PS: My install passed inspection by the local building enforcement and he was an electrician before code enforcement. I explained it and why and he looked at the UL sticker and agreed that was the correct and only safe way to do it and signed off.)
And by tell us, draw the circuit that you think would cause what you claim and I’ll hook it up and report back the results of whatever you tell me to measure to the group. This is straight forward to test because it’s trivial to craste low voltage versions of the US grid. In fact Tesla himself, when he designed it, did exactly that.
But again, you’ve provided no evidence of your assertion at all. Nor has anyone else in here for that matter.