Thank you for the thorough explanation. Our place is completely off grid. Closest power is 3 miles away as the crow flies. So the only thing I have hooked to AC1 is a generator inlet for a 2nd generator that never gets used (redundancy only). All AC coupling, grid sell, load shave, etc. is disabled.On the XW-Pro, there are two sets of different settings. There is "Generator Support" for the AC2 input, but it also has "Grid Support" settings for the AC1 input. My XW-Pro operates in a combination of "Grid Support" and "Sell to Grid" every night after 4 pm as the sun goes down.
"Generator Support" is very simple, with just a switch for enable/disable, and a current level setting for how much current it will allow from the generator before it begins covering the difference.
"Grid Support" is a lot more complex. Look in the XW+ settings. Do you see anything called "Grid Support"? It has 3 separate power settings. "Load Shave" is the basic equal to "Generator Support" where it will use battery power to keep the grid power draw below this set current level. But in my use case, I have Grid Sell active, so it overrides the Load Shave. Instead of waiting for the load to exceed a set current, it exports the desired current back to the grid. For it to do that, it first must supply all of the load on it's output. So that make the Load Shave do nothing.
What are you trying to make the XW+ do? If it does not have Grid Support, can you put the grid on the AC2 input and use the "Generator Support" to give you the grid support you need? Here is a screen grab of the config menu on the XW-Pro in Advanced mode
Once I click on the Advanced tab at the top, the generator support tab appears after the grid support tab. The Grid Support tab is actually there in the basic mode. So I think the XW+ likely has it too. I just checked, and when in Basic Mode, it has just 2 options like the Generator Support. Enable/Disable and the battery voltage above which it will function. You have to go into advanced to adjust the current.
The biggest difference though is that Load Shave and Grid Sell also have time settings for when they are active or blocked. Generator Support is just on or off as you set it, no timer.
Since my system also has up to 3,900 watts of power coming in to the XW-Pro output from my AC coupled Enphase microinverters, the "Sell to Grid" acts a bit different, but actually very smart. The XW-Pro is always measuring how much power is flowing in or out of the AC1 port. If I command it to "Sell" 2 amps back to the AC1 grid port, it will adjust the inverter power to hit that number at the AC1 port. But this is where it get's smart. If my Enphase inverters are already pushing 1 amp out the AC1 port, it will only add the additional 1 amp to make the total 2 amps. For my system, this is important because I am measuring the power my home is using from the main panel and commanding the XW-Pro to supply that power. The XW-Pro can only do this with an added power meter. The built in software directly supports this function with a "Watt-Node" power meter. I am doing it with a pair of cheap power meters and a PLC that I programmed. @400bird on here is doing something similar with a Raspberry Pi. Right now, the sun is still shining and my Enphase system is able to fully power my house, even the loads back in the main panel, and my battery is completely full. So the XW-Pro is sitting idle even though the house is asking for power out of the main panel. It's getting that power from the Enphase system, not from the batteries. In less than an hour though, the sun will be too low, and the XW-Pro will start to ramp up and use battery power to keep running my house with the grid power being held to basically zero.
Running the loads, the XW-Pro is very smart and capable. BUT... When it comes to charging from the AC coupled grid tied solar, it's not so smart. There is no setting in the XW-Pro that will make it start charging on it's own from AC coupled solar. There are a few ways around this, but the best is with an external controller that can detect when the Grid Tied AC coupled PV is making enough power and then have that command the XW-Pro into Bulk Charge and adjust the current to suit. There is no reason the XW-Pro couldn't do it with just the "Watt-Node" connected, but the software just is not there to do it.
Sun Power is selling their own "SunVault" storage system. But when I watched their video, sure enough, there is a Schneider XW-Pro inside their giant cabinet. Their system controller is evidently doing basically the same thing that @400bird and I are doing with his Raspberry Pi and my Nano-10 PLC.
I'm thinking of hooking the Pro Power 7.2kw inverter in the bed of my F150 Lightning to AC2 and use gen support plus if needed. I'm a little worried from other posts that somehow the XW+ could back feed the Lightning and damage it somehow. I can't wrap my head around how that could happen using AC2. Never been a problem with my 5kw diesel genset. But the Lightning cost significantly more so I'm being ultra cautious.
In any event I have a 1050w 48v golf cart charger that goes directly to the batteries so I will try that first with the Lightning to see if 22a charging at night is enough to supplement my 280ah Lishen bank when my wife goes crazy with 120v kitchen appliances. If I need more I'll look into the AC2 input method. If it's safe to use the Lightning Pro Power on AC2 I'll install a simple transfer switch and use it so I can hook my diesel genset or my Lightning to AC2 and utilize gen support with either.
The diesel genset is in the garage and exhausted out a thimble. I don't like running it at night when we are trying to enjoy the evening. It's pretty quiet but the garage is attached so it certainly can be heard. Outside you can barely hear it. We are in prime elk habitat and I hate it when neighbors run their loud ass gensets. You can hear them over a mile away.