Nice function, but.. if you are looking at the official documentation rom Schnieder, it includes the hex and dec addresses
ah..multiple docs - was looking at another, 1 does not have the dec code. With this doc -1 as per your writeup...coolNice function, but.. if you are looking at the official documentation rom Schnieder, it includes the hex and dec addresses
Do you have BMS communication set up? If so the BMS is dictating the charge cycle.few more questions..
- I have my batteries(eg4) set to 3 cycle charging but I am not using SOC so how does it know when to stop bulk charging? The voltages are based on eg4 doc (56.2 for bulk/absorb, 54v for float). The voltages never get to these values. SOC gets to 100 before voltages. Should I switch them to 2 cycle - default?
60 amp AC breaker? I'm not sure the alarm is related.I think the 60A breaker tripped yesterday with this error but my HBCO is at 58. Not sure how it tripped
Cause: Battery voltage is (BattV), which is approaching the High Battery Cut Out level of (HBCO). Solution: Check battery cables. Check for the correct battery voltage at the inverter's DC input terminals. Make sure the DC source is regulated below the high battery cut out or increase the High Batt Cut Out setting.
So when this happened, the charge cycle was set to External BMS as I do have closed loop communications but have not used SOC yet. I then changed it to 3 cycle. On 3 cycle, it kept on charging till 98% before I turned it off as I did not want it to trip. I received 4 alarms with External BMS set. I thought maybe the first one as the issue. Here are the 4 alarmsDo you have BMS communication set up? If so the BMS is dictating the charge cycle.
ah..maybe the first event in my image...approaching HBCO..but there is no time difference between that event and other events60 amp AC breaker? I'm not sure the alarm is related.
I've posted here before, this is the "warning" alarm that sets 3 volts below your HBCO to give some warning that the voltage is getting high. I really wish they'd include that info somewhere.
At least, they improved the fault text, it used to say 68 volts!
They do recommend 2 stage when I had talked to them.I've never tried this, so grain of salt:
It is my understanding from the documentation that if you want to use Enhanced Grid Support, the inverter charger needs to be set at 2 stage (and if you have Schnieder charge controllers, those get set to 3 stage). (I don't use the charger built into the inverter, so this is purely an opinion from reading the docs. My suspicion is, if the inverter never leaves "charge" mode, then it can never actually enter invert mode to start selling back excess PV)
soc -- I will get thereSecond, If you are using SOC control (and you should, if you have closed loop comms) the BMS will tell the schnieder gear to ramp down it's charge current as the batteries near full. Pure assumption here, but.. make sure your batteries have the latest firmware, so they top balance correctly. When I've seen the "DC Over voltage" when the batteries are nearly full.. it was due to the cells being imbalanced (older battery firmware) and one of the packs would hit a cell overvoltage limit, and the BMS for that pack would stop accepting a charge.
Interesting, yeah, that makes senseFor a brief moment, the current that was going to that pack had to go somewhere, so the DC bus saw a massive voltage spike. Thus the alert.
I have the latest firmware on batteries and inverter. I will try out some of the things you mentioned.I would break out the BMS utility on your computer, let the batteries charge to 98% or so, and then check cell voltages. Check all the packs for any internal alarms, etc. But also check the firmware, and get them updated if they are older.
I think the 60A breaker tripped yesterday with this error but my HBCO is at 58. Not sure how it tripped
60 amp AC breaker? I'm not sure the alarm is related.
You never answered which breaker, but seeing the faults, looks like it was a 60 amp AC breaker.
I missed the part about a breaker tripping.You never answered which breaker, but seeing the faults, looks like it was a 60 amp AC breaker.
I guess I was wrong and they are related. I'd spend time figuring out what's going on with your loads to trace down why the breaker tripped.
sorry, yeah, it is the AC1 IN breaker.You never answered which breaker, but seeing the faults, looks like it was a 60 amp AC breaker.
I guess I was wrong and they are related. I'd spend time figuring out what's going on with your loads to trace down why the breaker tripped.
:-( ok. Will doI missed the part about a breaker tripping.
I'm with 400bird here. breakers tripping is a huge red flag. Figure that out first, before any of the "nice to have" settings.
Shouldn't trip that breaker as the XW monitors input current and has settings to avoid tripping the AC breakers. It should lower charge current to stay below tripping the breaker.External BMS was set. With External BMS, the Max Charge takes effect. If at max (140A) and a single battery, would that trip the breaker?
sorry, yeah, it is the AC1 IN breaker.
External BMS was set. With External BMS, the Max Charge takes effect. If at max (140A) and a single battery, would that trip the breaker?
my charging is always from the grid as I don't have any solarShouldn't trip that breaker as the XW monitors input current and has settings to avoid tripping the AC breakers. It should lower charge current to stay below tripping the breaker.
Also, 60 amps x 240 vac = 14,400 watts
140 amps x 60 vdc = 8,600 watts
But, were you charging from the grid? If not, then the charger isn't putting any current through the AC input breaker.
I only have few circuits which pull in about 300w (tv & lights). The only time it trips is when charging and the current on the inverter shows going up to 70+ amps. I will check my wires though and I have also sent an email to schneider on the loose sleeve on the cable inside the inverter that @n2aws pointed out. I checked and that looks ok as it is only the sleep. Connections seem fine but will need to double check. Thank youIf you had been running near 60 amps AC for hours, maybe. But, without more data, I'd be more inclined to think some large load started with too much else already running.
breaker on the main panel and sub-panel is 60A and the wires are 6 awg. Load is around 300w.Not unless you also had something like 7,000w of load, in addition to the 140a charging.
140a x 51.2v = 7168w (I went with nominal voltage just to show the math)
60a x 240 = 14,400 watts (again, nominal)
So assuming your wires are properly sized, and the breaker is 60amps.. at "full throttle" charging of the batteries, you still have roughly 7,000 watts available before that AC breaker should trip.
yeah, need to go thru it carefullyI'm concerned you may have something else going on, other than just settings in the Schnieder stuff. I'd hate to see a shock or fire hazard, so yeah man, focus on that first. Also, I'd strongly encourage you to find the root cause if at all possible. I'm not a big fan of "well, it must have been a 1 time freak thing" with stuff like this. It tripped for a reason. Too much current, too much heat, loose connections causing arcing (if it's an arc-fault breaker), breaker failing/going bad.. etc. *something* caused it to trip.
Does your 60a breaker provide power to anything other than the inverter? like maybe a loads panel or something? Any way additional current would be going though that breaker, that *is not* being used directly by the inverter or passthrough?
no. So the 60A from main panel is dedicated to the inverter. The inverter feeds a sub-panel which also has a 60A breakerDoes your 60a breaker provide power to anything other than the inverter? like maybe a loads panel or something? Any way additional current would be going though that breaker, that *is not* being used directly by the inverter or passthrough?
main(60a) --> inverter with mini-pdp breaker(s) --> sub-panel(60a)Something is seriously wrong for that 60 amp breaker to trip. Where is this breaker? Is it in the Schneider PDP or is it back in your main panel?
IS the breaker getting hot? I would suspect a bad connection of failing breaker. Do you have a clamp on amp meter? Measure the current at that breaker. Check both legs.
I only have a 20 amp breaker on the input of my XW-Pro because of my 120% rule back to my 100 amp main panel. I have never tripped that breaker.
Simlarly, I only have a 30a breaker for my input (long story.. I repurposed an existing subpanel to become the critical loads panel, but used the existing wiring which is only rated for 30a.. and I'm waiting until winter time to do the attic work of replacing the wire with thicker.. so I've dropped the breaker to 30a)I only have a 20 amp breaker on the input of my XW-Pro because of my 120% rule back to my 100 amp main panel. I have never tripped that breaker.
My system does indirectly power my A/C system.>I only have a 20 amp breaker on the input of my XW-Pro because of my 120% rule back to my 100 amp main panel. I have never tripped that breaker.
Interesting. My plan was to run my AC units