can you use Schneider with enphase grid tie system , like ac coupling?I have a Sol Ark 12K. I would do it again for my particular situation. I think the Schneider is more capable inverter overall, but it has a lot of separate components that need to be configured by someone who knows what they are doing, and as a rank amateur diyer, I was concerned it would be too hard to commission. I know I could have eventually gotten it to work but, it’s definitely oriented toward a trained installer. My Sol Ark handles my 500 ft deep well pump just fine. Never even seen it flicker. I’m totally off grid. I think having a large enough battery bank is important too to handle surges. I literally hooked mine up in two hours and it was the first “real” inverter I’ve ever installed. It’s run perfectly since then.
For someone who wants the best and is a tinkerer/perfectionist, the XW is the way to go. If you want an easy, trouble-free install, I’d suggest the Sol Ark series.
If I was paying an installer, I’d definitely have gotten an xw, however, hehe
can you use Schneider with enphase grid tie system , like ac coupling?
I can really appreciate a company that under-promises and over-delivers. There should definitely be more companies like this.I believe the newer 6848 is the same thing internally as the 6048, they just changed the face plates to go from the Xantrex to the Conext branding. And upped the continuous rating because the older 6048 was actually derated and will easily put out 6,800 watts in overload without breaking a sweat while maintaining perfect 60Hz and 240V phase to phase.
Not sure what class you are referring to? I think everything you mentioned, the Sol-Ark is capable of.are these SolArk inverters being discussed even in that same class?
Not sure what class you are referring to? I think everything you mentioned, the Sol-Ark is capable of.
23 years of daily use on two of it's ancestors, the Trace SW4048.As C&K said, there is no other inverter with this kind of performance history when you are looking for something dependable. Mine has been in service for nearly 3 years without a glitch or issue. I expect to get at least 20 years out of it as many others have. They have an impressive history- research the Trace/Xantrex/Schneider history for some great info. As with any quality electronic item, you get what you pay for.
I wonder how many growatt or eg4 owners will be able to say the same after 10 years of ownership?
Knowing that you have the expertise and skill to set everything up properly with no weak links, i'd say you have the best chance to keep 'em going for a long time!I'll let you know......... hopefully.
Like @OzSolar said, it does have generator exercise and basic setup, but I do not think it will control 2x generators. I'm not too sure, as I have never looked into generator usage, and dont really have a need for it.
Sol-Ark is the same as Outback. Either on or off based upon battery level. They do offer "grid peak shaving", which prevents generator overload. You should ask Sol-Ark to enable "Gen Start" when near Overload situation.Does the Sol-Ark have proper generator support for auto-starting twin generators, used for different purposes in off-grid applications?
It manages both generators automatically with fully programmable AGS for starting diesels, something Outback never was able to accomplish since they only ever supported a simple two-wire generator starting system that requires external logic controllers on diesel generators.
You should ask Sol-Ark to enable "Gen Start" when near Overload situation.
I wonder if SMA can do this? Off to dig through the manuals.You mean this is a feature that can be turned on? Or it's a feature that needs to be implemented yet?
This is our most commonly used feature, is generator support. If the load exceeds 48 amps on either leg for more than 15 seconds it will start the peaking generator, allow it to warm up for 15-20 seconds, then load it to whatever you set it for. In our case the breaker on the generator is 28A, so we have the settings in the inverters to load it to 25A, which reduces the load on the inverters to 23 amps. The inverters automatically balance the legs on the generator so it can put out full capacity, even though the load on the AC output of the inverters might not be balanced.
If the load drops below 48 amps on the highest leg for more than 5 minutes, then it shuts the peaking generator down.
To my way of thinking, this is the single most important feature for an off-grid inverter. Without it you are limited to only what the inverters can put out and requires a huge expense in extra battery and inverter capacity, as compared to a fairly cheap peaking generator, for very intermittent high loads on your system. It removes all the hassle with worrying about overloading your off-grid system - just turn on what you want and the system will take care of it, automatically and seamlessly - the lights don't even flicker. All you have to do is properly size your peaking generator for the highest expected overload. We have never found an instance where the inverters can't handle even a 18kVA load for the minute or so required to bring the peaking generator online. In the winter time that little Perkins diesel is kept plugged in and warmed up to operating temperature 24/7 just for that purpose.
This was designed by some brilliant engineers (at Xantrex - Schneider did not invent this, it was there before they bought Xantrex) that truly understand how high-capacity off-grid systems need to work. If the Sol-Ark can't do this, it is not even in the running to replace 6048's. That is why I asked if those Sol-Ark are in the same class as a XW-series for off-grid applications.
SMA really should hire you lol.Sunny Island can take input of say 15A from a generator (or grid) and add amps from battery/inverter to support additional local consumption
It can call for generator start when battery SoC gets low (plus time of day/not modifications to the SoC which triggers it.)
Start generator above some current draw? I'll have to check manual.
"14.1 Generator
The Sunny Island can start or stop a generator depending on consumer power or battery state of
charge. In this case, diverse limits and times are taken into consideration
(see section 14.1.5 ”Automatic Generator Operation” (page 122))."
"Load‑Dependent Start
In case increased energy demands arise, the generator can be requested for support. This function
can be switched on or off (default) using the "235.09 GnPwrEna" parameter. The function is only
effective if the "235.01 GnAutoEna" parameter is simultaneously set to On.
The load limit for the request and the generator stop is configured using the "235.10 GnPwrStr" and
"235.11 GnPwrStp" parameters. The average time by which an average value for the consumer
power is calculated can be set using "235.12 GnPwrAvgTm". This prevents temporary power
consumption peaks of a few seconds from causing a power‑dependent generator start.
If the generator has been started due to the load, it runs according to the minimum generator run time.
If, once this time has expired, the average power is below the cutoff limit, the generator is stopped
again."
"10 GnPwrStr Generator request switch‑on power limit [default] 4 kW "