Not sure if this is a "thing" or not ...
1 combiner box with 2 outputs to two separate charge controllers and 1 shared neutral ... like a 2-2-4 AL URD cable to blocks torqued to spec with copper going the rest of the way.
If someone did this would you calculate voltage drop using the 4awg wire with both loads?
I have only ever seen non-shared neutral wiring from combiner boxes and was wondering, since they tie to each other in the panels, if this was possible and if so what it would mean for voltage drop since you would have less cross sectional wire on the neutral side of the circuit.
1 combiner box with 2 outputs to two separate charge controllers and 1 shared neutral ... like a 2-2-4 AL URD cable to blocks torqued to spec with copper going the rest of the way.
If someone did this would you calculate voltage drop using the 4awg wire with both loads?
I have only ever seen non-shared neutral wiring from combiner boxes and was wondering, since they tie to each other in the panels, if this was possible and if so what it would mean for voltage drop since you would have less cross sectional wire on the neutral side of the circuit.