... my coffee shop experience short power cuts around 20 mins, 30 mins or 1 hour. ...how I can set this up for under $1,000?
Old post, sorry I didn't see it back in Feb. But... solar is attractive and can reduce your power bill. I definitely recommend it.
Goal
But, it sounds like your actual goal is to keep the lights on when the grid goes off, and that can be done for under $1000 with either a battery or generator backup. So, I suggest ignoring solar panels for your goal. Instead, ask how much can be backed up for about $1000? Let's see...
Power Budget
The first thing to understand is your actual power needs. You have a good start in knowing your coffee shop consumes 5 kWh/d and the list of devices:
Item | quantity | Watts | Total watts | Total kWh (to cover 60 min outage) |
Small ceiling LED light | 10 | 10 | 100 | 100 |
Nouva Simonelle Appai II Compact | 1 | 3000 | 3000 | 3000 |
1HP inverter Aircon Panasonic | 1 | 2500 | 2500 | 2500 |
Grinder | 1 | 300 | 300 | 300 |
small Ice Cream fridge | 1 | 46 | 46 | 46 |
That's a maximum. Truth is things like the fridge and air conditioner come on and off, that is, they're not always running. Ultimately, it's up to you as to what the absolute minimums are when the grid goes out. With the heat you've been having, perhaps keeping the AC on brings a lot of customer loyalty...but, even though it's a minisplit, it's probably going to need a 4 kW surge capable inverter and in an hour outage might run for 30 minutes (1500 wH), which is going to require a larger battery.
Options
The total is about 6 kWh, but for an hour-long outage, what devices do you really need to run and for hour long? For a gasoline generator size, you need the total watts for normal draw plus any startup surges that can occur simultaneously. You might be able to get away with a 5 kW generator, but even 10 kW generators can be found for under $1k. But, gasoline generators are noisy and need fuel. If you have natural gas or propane available, you can do away with the inconvenience of storing and transporting gasoline. Unfortunately, it would have to be run outside making it a target for thieves (possibly it could be installed on the roof?).
So what about a battery? For under $1k you'll need to make some tough decisions. For example, could you get a
small battery grinder for beans? Will the freezer stay frozen for that hour? If so, you don't need to power them, you can let them ride through the outage.
How many battery W & Wh for $1k?
You can probably get an inverter, battery, and charger piecemeal and put them together for a better price than a solar generator and Will's links at the top of the page will show you how to do that. But, working backward from a budget of $1000, a
RockPal solar generator is about that price and provides
1300W and 1254 Wh (if for simplicity you do decide to go for a solar generator be sure to pick one that works with the voltage/phase of your country). Others on the thread can probably give you better ideas as to devices and costs, I just tossed out the first thing I saw.
How to Wire it
In terms of wiring, you'd plug your system into the grid, then plug the devices to be backed up into your system. Devices without plugs (e.g., Ceiling lights) and wall outlets can be setup by installing at your breaker panel with either a
transfer switch or inexpensively with appropriate 3-way switches.
Ask if you have more questions.