Connect them where the external CTs for the grid connect. The UI menu would tell the Sol-Ark if the CTs are deployed to the Grid or the Gen input.And connect them to what ?
Connect them where the external CTs for the grid connect. The UI menu would tell the Sol-Ark if the CTs are deployed to the Grid or the Gen input.And connect them to what ?
Because a generator AC input port must not allow back fed power there is no advantage to having CT sensor outside of inverter.If your observation is correct, they could resolve this by using external CTs on the Gen input.
Sol-Ark already supports and recommends generator connected to the grid using external CTs. Doing the same on the Gen input wouldn't be different. AFAIK Sunsynk doesn't have any internal CT on the Gen input and they support Gen peak shaving using external CTs. Gen peak shaving is a setting in Powerview.Because a generator AC input port must not allow back fed power there is no advantage to having CT sensor outside of inverter.
For practicality, it is bit better to put gen port CT sensor internal to ensure it works properly to prevent back feed then rely on installer/user getting the external CT sensor hookup correct. It is too easy to put CT sensor over sensed wire backwards. Long, poorly dressed CT output sense wire pairs affects the measurement accuracy of phase and current. Correct phase relationship to AC voltage is critical to determine power flow direction.
Factory can better calibrate an installed given internal CT sensor then rely on separate external CT sensor with its random make tolerance accuracy.
Inverters with external CT sensor capability usually hold a reserve margin on sensed current of a few amps positive power from utility incoming power to ensure accuracy limitations of external CT sensor power flow direction and magnitude measurement does not result in some grid back feed power when zero grid export is set in inverter.
This is true except for the fact that the Sol-Arks don't limit the draw from the generator. Schneider, Outback, Magnum, etc. all have either input amps or breaker size setting. This allows the inverter to dynamically control power being drawn from the gen. E.g. as loads go up, the inverter dynamically controls the charge rate to keep the amps flowing into it at the setpoint that it has been configured to, and to avoid overloading the gen.Because a generator AC input port must not allow back fed power there is no advantage to having CT sensor outside of inverter.
The external CT sensors currently coming with the Sol-Arks do need to be installed correctly. But this goes for any CT sensor application that is to read bi-directional current! The bigger, reputable, name-brand AIOs such as Sol-Ark, Eg4 (18kpv), LuxPower, etc. all come with external CT sensors that are optional. The instructions for setting them up always mention that they have to be installed correctly to work right! With external CT sensors, you get additional features, at the cost of having to install the optional CTs correctly. To me this is a very small cost for the added benefits available!For practicality, it is bit better to put gen port CT sensor internal to ensure it works properly to prevent back feed then rely on installer/user getting the external CT sensor hookup correct. It is too easy to put CT sensor over sensed wire backwards. Long, poorly dressed CT output sense wire pairs affects the measurement accuracy of phase and current. Correct phase relationship to AC voltage is critical to determine power flow direction.
The Sol-Ark inverters have a setting to set the minimum draw from grid between 0-500 watts. Even when set to 25 or 50 watts there tends to be some short spikes of power that flow back to grid. I am sure that even clouds passing in front of the sun can affect the power flow enough to make it hard for the inverter to respond quickly enough!Factory can better calibrate an installed given internal CT sensor then rely on separate external CT sensor with its random make tolerance accuracy.
Inverters with external CT sensor capability usually hold a reserve margin on sensed current of a few amps positive power from utility incoming power to ensure accuracy limitations of external CT sensor power flow direction and magnitude measurement does not result in some grid back feed power when zero grid export is set in inverter.
Thanks for that! Although it looks like it is a 2021 document, so I don't believe that gen shave is able to use the external CT sensors anymore. I could be wrong though, so I might give it a try to see for sure.Found this in the PowerView document. The PV settings document explains things so much better than the Sol-Ark manuals.
Even if it is accessible through PowerView, almost for certain access will be gone when we migrate to MySolArk monitoring in May.Thanks for that! Although it looks like it is a 2021 document, so I don't believe that gen shave is able to use the external CT sensors anymore. I could be wrong though, so I might give it a try to see for sure.
You stated that in off grid you can use grid peak shaving to limit gen draw. So when the gen is connected to grid input you turn off “gen peak shaving” and select “grid peak shaving?” I am having an issue where the inverter is overloading the generator even though I have Gen peak shaving set at 12,000 watts for a 14,000 watt generator. I spoke with tech support and they went through my system but due not change the Gen peak shaving to grid peak shaving.Just a heads up to anyone who may have questions and/or issues with the gen input and gen shave function!
According to Sol-Ark tech support, the gen shave function is no longer supported. I am quite confused as to why they would drop that! (Especially since it is still in the menu!) It is a very important part of using the gen terminals for gen charging!
The idea is that you set gen shave to whatever wattage that your generator can comfortably handle, then the inverter adjusts the charge rate in realtime as your passthrough loads go up or down, to maximize gen usage during gen run times, while avoiding overloading and/or low voltage or frequency because of the generator being close to overload.
I'm sure someone will say "adjust the 'gen start A' setting". But that does not compensate for fluctuating loads, and frankly, doesn't work well! I have seen this time and time again with many other brands of inverter! For instance, I have seen many Magnum inverters that had "shore" or "input amps" (depending on advanced remote or not) set to the full 30A with that max charge rate set to lower than 100% to compensate for a small generator. But the instant you have bigger loads kick in, the generator will either overload, or the voltage will drop and the inverter will disconnect. Then it will reconnect.... disconnect.... reconnect..... you get the point.
A breaker size setting or input amps (or watts) setting is always far superior. And really without that it is a disaster!
Note* in an off-grid scenario, you can still use the grid terminals and set grid peak shave to limit that generator draw! The issue is when you either have grid and want a backup gen charge option, or when off grid with a hardwired gen on grid input, and you want a portable charge option on gen terminals.
Note #2* Don't bother mentioning that you can use a standalone charger. I am aware of this. In fact the Eg4 Chargeverter is my go-to option for that. However, the fact that the Sol-Ark inverters physically have the capability to use a generator on the gen input terminals, but the software is simply not programmed to handle it correctly, is what makes no sense to me.
Also, the point of this thread is to make others aware, and perhaps shed some light on any issues that others may have with the gen input and the gen shave menu item.
Here is a screenshot of my conversation with Sol-Ark tech support where I was made aware of this:View attachment 199003
Which generator specifically? Perhaps 14kw surge with a lesser continous rating?You stated that in off grid you can use grid peak shaving to limit gen draw. So when the gen is connected to grid input you turn off “gen peak shaving” and select “grid peak shaving?” I am having an issue where the inverter is overloading the generator even though I have Gen peak shaving set at 12,000 watts for a 14,000 watt generator. I spoke with tech support and they went through my system but due not change the Gen peak shaving to grid peak shaving.
On your Basic Setup screen, Advanced tab, what is you Gen Limit Power setting?I am having an issue where the inverter is overloading the generator even though I have Gen peak shaving set at 12,000 watts for a 14,000 watt generator.
Generac 14k. It states its 14k operating wattage, but I have it set to 12k limit.Which generator specifically? Perhaps 14kw surge with a lesser continous rating?
12,000.On your Basic Setup screen, Advanced tab, what is you Gen Limit Power setting?
On the Limiter screen, Other tab, "gen connected to grid" checked?12,000.
Yes, Gen connected to grid is checked. My AC units are soft start units that ramp up slowly. The generator is being kicked off when the inverter tries to pull over 14,000 watts when trying to supply power to an AC unit. The inverter never drops charging wattage, it tries to maintain the max charging amperage set in the battery settings no matter what the load is. Should it I have a 6,000 load, and max charging amperage set at 165, the generator is overloaded and the inverter kicked it off.On the Limiter screen, Other tab, "gen connected to grid" checked?
Sudden draw on generator? do you have Eco mode off (or whatever similar setting)?
Gen shave doesn't work. Period.You stated that in off grid you can use grid peak shaving to limit gen draw. So when the gen is connected to grid input you turn off “gen peak shaving” and select “grid peak shaving?” I am having an issue where the inverter is overloading the generator even though I have Gen peak shaving set at 12,000 watts for a 14,000 watt generator. I spoke with tech support and they went through my system but due not change the Gen peak shaving to grid peak shaving.
I think there was a discussion earlier that that setting is deprecated but still visible?I would try Gen Peak Shaving. See post 56 above. Gen Peak shaving is still an option in MySolArk. This feature utilizes the external CTs.
All hybrid inverters running in parallel with AC input source, whether high freq or low freg design, have an AC input tracking response time delay.The Sol-Ark inverters have a setting to set the minimum draw from grid between 0-500 watts. Even when set to 25 or 50 watts there tends to be some short spikes of power that flow back to grid. I am sure that even clouds passing in front of the sun can affect the power flow enough to make it hard for the inverter to respond quickly enough!
Unfortunately, unless someone is running very old firmware, the gen shave function no longer is capable of using the external CTs! It uses only the internal CTs, and as far as I can see on the circuit board, the internal "CTs" consist of a single CT, presumably monitoring only the amps draw of one phase. Therefore phase imbalance between L1 and L2 causes massive swings in the functionality of "gen shave" specifically.I would try Gen Peak Shaving. See post 56 above. Gen Peak shaving is still an option in MySolArk. This feature utilizes the external CTs.
Assuming you can live in the 12-14kW limit of the inverter, the next best option is to use 2 Chargeverters to directly charge the battery. Constant 8kW load on the generator.Yes, Gen connected to grid is checked. My AC units are soft start units that ramp up slowly. The generator is being kicked off when the inverter tries to pull over 14,000 watts when trying to supply power to an AC unit. The inverter never drops charging wattage, it tries to maintain the max charging amperage set in the battery settings no matter what the load is. Should it I have a 6,000 load, and max charging amperage set at 165, the generator is overloaded and the inverter kicked it off.
Why does this not work at any hour of the day and PV output? There should NEVER be any problem with overcharging, or you have misconfigured something.So instead I decided (see signature) to use alternate charging methods by using a cheap chinese inverter (better than a chargeverter, now I have a backup inverter if needed), to charge my batteries before the solark. Keep in mind that can only be done in the dark or WITH PV TURNED OFF ON THE SOLARK
All inverters have the problem of passing through dirty power (inverter has to match the generator). The only way around it is direct charging of the battery.i HATE the way solark uses my generator power.