I also am wondering what configuration of any panel is more efficient, higher voltage and less amps or max amperage and less voltage. I realize the wattage will figure up either way. Just wondering about the efficiency
For me there's a bit more that goes into the wiring and how many to put in series. I'll show you the way I calculated my using
This voltage loss calculator. The thickness, weight and cost of the wire from the combiner to the SCC made me not use the 6P configuration.
My calculations are very conservative, and some will find the wire size I end up with way too thick. I am happy with the results.
====================================================
For my six - 100 panel string on my RV build that always deals with shade, the most efficient way is as many in parallel as possible, until wire thickness gets too much for voltage loss, too heavy to put up, or too much of a loss. Another thing is the max wire gauge accepted by the SCC.
I decided I wanted a 3% total loss from panel to SCC. You could probably go higher. There were two legs: The first Panel to combiner, and then Combiner to SCC.
Panels accept up to 10 AWG cables for MC4, so loss on the panel to combiner leg is 10 AWG. With 20 volts, 6 amps, and 15 feet, the loss came out to 1.5%:
Now for the combiner to Battery portion, the voltage is still 20 volts, the amperage combines to 36 amps, and the distance is 50 feet. So, ampacity becomes an issue, and I want a minimum of 8 AWG wire for ampacity. Voltage loss will drive a higer than 8 AWG wire to meet a 1.5% loss, which comes out to 2/0. This is about $3.80 per foot.
===============================
You can also change the math around so that you accept more than a 3% loss, maybe 10% and the wires get thinner. Honestly, a 10% loss in production could equate to a charging time of 5 and a half hours with a 10% loss compared to 5 hours for a 3% loss.
a 10% total loss would be 10 AWG from panels to Combiner, and then 6 AWG from combiner to Battery:
============================
You could also choose to combine closer to the SCC and that would make the high amperage run shorter, or even work to get the SCC much closer to the batteries. Also, if you ever plan on going to 24 volts, you need to at least put the panels 2S to get enough voltage for the SCC to charge those.
===============================