How much load is going through your inverter when this happens?
What is the running voltage of the system during this testing (on a video)? What is the Min/Max voltage of the system during this test procedure?
Have you connected the windows software for BMS interface? This would show why the battery shutdown in its' errors. I haven't installed this software myself, and don't really want to install on anything other than a burner laptop, but it would be nice to know what alarm it shutdown over.
DC Ripple?
Based on the description of the issue you've given, which doesn't include much hard data, I'd go into your magnum battery charger settings and reduce the battery charger voltages a little bit, which could reduce the impacts of DC ripple, apparently being caused by either the transfer switch or battery charger operations in your magnum and the order in which it makes that change. Considering the charging voltage parameters aren't listed in your post and the running system voltages aren't shown on your video, I'm basically an alternate energy psychic if I actually got this right. Revert your modifications if nothing changes after further testing (but also make sure these settings are correct while you're there).
Have you tried shutting the charger off before disconnecting using the magnum control interface? What happens? Do you have the magnum control interface? This test could help isolate whether transfer switch or battery charger operation is causing the issue (or if it's the synchronized operation of the two).
Current Sharing?
The videos show that the batteries aren't setup for ideal current sharing. I'm surprised the seller hasn't pointed this out?
Current Sharing Better Fix:
Add busbars to tie your batteries together, connect your system to the new battery busbars instead of directly to the packs. This helps distribute the load to both batteries evenly. Position the connections so that resistance/distance between the inverter/loads wire is the same to each battery.
If you still run into issues with shutting the BMS down because of current sharing issues, get a clamp multimeter (or two) to show how many amps are going through each wire (system positive wire to battery one and the positive wire between battery one/two--then make a new video. This would document how many amps your system is hitting the BMS with--See if the seller agrees this is a suitable test procedure before investing time?
Current Sharing Not-as-good Fix:
Connect your system to the negative terminal of the other battery pack. This isn't as good as busbars, but it does encourage power to be pulled from both packs more evenly than connecting both the system positive and negative wires to just one battery.
I'd also tell you to get a heavier wire tying the batteries together, but that circuit breaker is in the way. I tried it myself with 2AWG 1FT and it wasn't a good fit, decided to go with the included 6AWG for now until busbars, but that's not as good an idea on a 24v system (these 6AWG wires are for connection to busbar).
Full disclosure, I'm operating my 51.2V Lifepower4 packs in the "not-as-good" configuration, with the loads positive wire on battery 1 and the loads negative wire on battery 2. That's because I need to buy busbars still. The Lifepower4 48v/51.2v packs I'm using are good for twice as many watts power output as the 24V, and you're running a higher wattage inverter than I am also, you're 2-3 times more likely to hit BMS overload given the exact same system loads.
That's a long post so I will try to give it a good response.
The system load is minimal. This is an RV, which separates out small 12V loads for lights, fans and other on demand needs like awnings or heater fan.
The 4000w 24v inverter handles the 120v loads like TV, Refrigerator and 120v outlets.
The system minimum voltage is 12v and max is 120v. In the video you are looking at a 24v DC system.
I have connected the BMS software to the batteries and found it to be very clumsy at best. Its software from the 80s asking for baud rates and port configurations! Although I was able to get it to connect to port 3 eventually, I was not able to pull in any battery data. At the end of the day, I could see it was the batteries tripping. The batteries were replaced by other brand name and types and operate without failure. That pretty much indicates its a battery issue. As a consumer, I am not going to play repairman on a newly purchased product. It either works or it doesn't.
The magnum battery charger was off. The magnum inverter was on. There was no DC load charging the batteries from the inverter at the time the AC was disconnected. The solar charge controller was also turned off in the video when the AC was disconnected. This, in fact, was how the problem was originally seen. The AC load that was connected was a 20A power cord. That being said, I was not pulling 20A. When my A/C units are off, I rarely pull more than 15A for the entire RV. Only when high draw appliances, like coffee maker, air fryer, A/C are in do I pull significant Amperage.
I do have the magnum BMK(battery monitoring kit) and the MC-50 control interface, which reported a "dead battery" fault and the inverter would not power on. As you can see in the video, the batteries tripped which is why it was giving that fault. The MC-50 provides me with very detailed amperage, voltage, and temperature data, better than an amp clamp. It basically said, "hey dummy, the batteries are not working. Did you power them on?"
I am aware that I do not have the batteries connected to the bussbar. There is one in use. The factory cables were not long enough to reach. And since its more important to have same length cables, I chose to stack the connection until I can build longer cables. But it is for two batteries, which will not cause significant issue in charging. This would not be the cause of the issue. It only introduces inefficiencies in charging and discharging.
Signature solar has already acknowledged this is a BMS issue. I am not the 1st customer to have this problem, and it has already been resolved by using a different battery with a different bms. Richard indicated they are working on a solution, maybe a firmware upgrade for the BMS?
I wish I could be the one that could provide a technical explanation to others on this forum so they could prevent or fix it if it happens to them. Unfortunately, I am not Will Prowse.
I would offer that these batteries with this particular BMS is most likely optimized to work with EG4, MPP and Growatt inverters. When customers, like me, use them with other brands, unforeseen errors can and do occur. That being said, Signature Solar does have a "bare bones" compatibility test with my inverter brand (not the exact model), but the issue that is arising was not introduced in their video.
Thank you for your questions and input.