I'm curious if anyone has used a split bus panel and had it pass inspection. The interwebs points to 408.36 of the NEC but I don't see any issues with this setup so long as the backfed breaker has an additional fastener per (D) and confirmed by the manufacturer.
This configuration would give you the benefit of a single panelboard to function as the main panel and the critical loads panel. If you need to do maintenance on the inverter, you use the maintenance bypass breaker by shutting off the inverter output breaker and turning on the bypass breaker.