I'm not sure this is a "real" stress test because I didn't break it, but wanted to share my results from my stress teset today. I was impressed with Rosie.
Load:
13859W on AC, 12370 on Battery (something finished or turned off)
Things providing the load.
2 4gal bosch water heaters (1440W each)
1 5 ton air conditioner (observed 3000W)
1 20 btu mini split (observed 1920W)
1 Fortress 1.6 HP air compressor (1000W observed)
1 Metabo .15 HP air compressor
2 1500W space heaters on high heat
1 heat gun on high
Microwave
Lots of lights and house fans (most of my lights are led)
3 ceiling fans
Stove vent fan on high speed
The highest load I noticed on the MNGP2 was 13859W. Well within 2 Rosies.
At 13895W, that's 57A, so close to the 1 breaker that is served from a stacked set of Rosies (which is too small in my mind)
Max battery consumption 255a (across both Rosies)
2 alarms. 2 L2 OverCurrent error on both Rosies and Grid Disconnect Warning.
Zero issues switching from AC to Battery and Back (a couple of times). Maybe some slight led flickering in my garage lights.
Load:
13859W on AC, 12370 on Battery (something finished or turned off)
Things providing the load.
2 4gal bosch water heaters (1440W each)
1 5 ton air conditioner (observed 3000W)
1 20 btu mini split (observed 1920W)
1 Fortress 1.6 HP air compressor (1000W observed)
1 Metabo .15 HP air compressor
2 1500W space heaters on high heat
1 heat gun on high
Microwave
Lots of lights and house fans (most of my lights are led)
3 ceiling fans
Stove vent fan on high speed
The highest load I noticed on the MNGP2 was 13859W. Well within 2 Rosies.
At 13895W, that's 57A, so close to the 1 breaker that is served from a stacked set of Rosies (which is too small in my mind)
Max battery consumption 255a (across both Rosies)
2 alarms. 2 L2 OverCurrent error on both Rosies and Grid Disconnect Warning.
Zero issues switching from AC to Battery and Back (a couple of times). Maybe some slight led flickering in my garage lights.