Here's how I intend to wire up for Split-Phase 120V~240V 60 HZ application.
View attachment 121002
16K LOAD output L N wired to the Victron 100A Autotransformer L N 100A double pole circuit breaker
View attachment 120996
Victron 100A Autotransformer ?
Earlier this year, there's a big discussion about installing of the Growatt ES500 with SolarEdge 5KW Autotransformer and the issues of Ground Bonding issues. Questions of Losing the Neutral when the Autotransformer is down and damages that will be cause to all 120Vs circuit breaker on the LOAD panel, suddenly becoming 240V and damage/frying to all 120V connected appliance. There were suggestions of using 2 Autotransformer and using relays to monitor the Neutral line and so on. Just a complex mess and no real solution to the problem when loosing the Neutral wire.
Well, in my application, with a larger 24K Autotransformer load balancing the LOAD output of the Deye 16K's 16KW, The LOAD panel will be wired directly from the Victron's output L1, L2 and N terminals. As such if the Victron or the Deye 16K is down, all circuits on the LOAD panel will be down automatically, period. No damage will be caused to both the 240V and 120V circuits. The Victron has a built in Earth/Ground relay, allowing for Neutral to Ground bonding. Simple and Elegant solution to a Chicken or an Egg problem ???