The current model of the 16K com board DOES NOT have pin 19,20 for 230V ~ to drive an external relay for Neutral to Ground Bonding. The confusion arises from the documentation screen shot attached, that referenced the word "ATS" (Auto-Transfer-Switch). If you read carefully between the lines in the highlighted block of text in Yellow, the ATS logically refers to the G-Start port 7,8 when the "Signal ISLAND MODE" is CHECKED in the Advanced Function Menu. If the GRID is connected and is UP, it will output 230V, which then will be connected to an External Relay that will be Open and thus Disconnect the Earth-Neutral Bond. You need to read page (10) 3.3.2 Function port definition and page (34) Advanced Function
Documentation written by morons. I'm surprised the SynSynk is Not much better than the original docs with fuzzy mumbo jumbo description on the Earth to Neutral bonding. ?
SunSynk docs are no better than the Chinamen's version. Bunch of mumbo jumbo.
View attachment 136275
Page 34 of the Original 16K User Manual
View attachment 136269