this is exactly how I did it and it is currently working as intended. Nice one for making the diagram that will save a lot of people a lot of time!The documentation from Deye and SunSynk has done a pretty bad job in describing how to perform a Neutral to Earth/Ground bonding when the 16K Hybrid Inverter is operating in "Island Mode" (When GRID is disconnected) and needs N/G bonding.
Keith from SunSyn has posted a YouTube video that describe on how to wire up a N/G bonding, without a schematic and is difficult to implement.
It's said Picture means a thousand words. So here we are, below is a picture of how to wire up a Neutral/Ground bond using a standard "Normally Open" contactor.
1. The example uses a 16 bucks din-rail "Normally Open" type Contactor available on Amazon.
2. Connector 7,8 a dry contact for Generator signal control line, will be used as the control signal for "Island Mode"
3. In the "Advanced Function" menu, CHECK the "Signal Island Mode".
4. When the #3 is enabled, the port 7,8 will be enabled to ON state when the GRID is UP. It will be OFF when GRID is DOWN.
5. You can use a multi-meter set to TONE TEST to confirm a continuality tone when GRID is up. NO tone when GRID is down.
6. In the diagram below, I will be using the EU standard wire color code. L=Brown N=Blue G=Green
7. A "Normally Open" type Contactor is used in this example.
8. Wire 7 to A2 (Neutral return)
9. Wire 8 to Neutral on the LOAD L,N input.
10. Wire N to R2 of the contactor
11. Wire G to R1 of the contactor
12. Wire L to A1 of the contactor.
Here's how this schematic works. When the GRID is connected and the "Signal Island Mode" is enabled in the Advanced Function menu. The port 7,8 signal will power the Contactor via A1 (Live) and A2 (Neutral return), which in turn will keep the R1 and R2 of the contactor "OPEN" and disabled N/G bonding. When GRID power is lost, power to the A1 & A2 will be lost and become "OPEN". The coil of the contactor will be CLOSED and R1 & R2 will be energized and bond the Neutral and Ground wire. When GRID Power is restored, which will take a minute. A1 & A2 will be ON once again and will disable R1 & R2; the N/G bond will be disconnected.
Hopefully, this will help the DIYer in the 230V world. In the US, the Neutral to Ground bonding is always enable by NEC code at the main entrance panel and don't have to worry about this. ?
View attachment 136766
Out of interest does anyone know what the option in advanced settings that is labeled: ATS with a tickbox next to it and on or off in a box next to it does? There is no mention of it in the manual at all? Should it be ticked or not? and what does the option for on/off do?