Hello everyone
I want to improve my wiring diagram.
1) Fuse sizing for each battery pack
The inverter is a Multiplus 12/3000/120
It's 3000VA, 2400W continous and 5500 peak.
According to my energy audit, max loads and the formulas I found on the forum and guides.
I took into account the inverter effiency for AC loads. 93%
I calculated 266 Amps divided by 3 battery pack. 89A max load per battery pack.
89 * 1.25 head room for the fuse = 111. The one just above is 125Amps.
2) Wire sizes for battery positive to fuse
For the wire size to fuse and positive post, I used the bluesea calculator. It suggest 4AWG wires. Up to 155Amps.
3) Wiring diagram
Any errors you can spot?
I want to improve my wiring diagram.
1) Fuse sizing for each battery pack
The inverter is a Multiplus 12/3000/120
It's 3000VA, 2400W continous and 5500 peak.
According to my energy audit, max loads and the formulas I found on the forum and guides.
I took into account the inverter effiency for AC loads. 93%
I calculated 266 Amps divided by 3 battery pack. 89A max load per battery pack.
89 * 1.25 head room for the fuse = 111. The one just above is 125Amps.
2) Wire sizes for battery positive to fuse
For the wire size to fuse and positive post, I used the bluesea calculator. It suggest 4AWG wires. Up to 155Amps.
3) Wiring diagram
Any errors you can spot?