The mosfet versus IGBT argument for inverters is interesting......
They both have advantages and disadvantages. For surge overload capability, IGBTs win hands down.
The reason for that is that mosfets when turned on act like low value resistors.
If you double the current, the voltage drop also doubles, and the power dissipated goes up four times.
A times ten surge current, and power dissipated goes up 100 times, and your mosfet instantly explodes.
An IGBT is different, in that the rated voltage drop at full max current might be a couple of volts, but it does not go up much higher than that at much higher current. So power dissipation tends to be very roughly proportional to current. A ten times surge overload, power might go up 15 times (as a guess) not to 100 times.
Diodes act in a rather similar way, you lose about 0.6v in the forward direction, but even with a massive current surge, its not likely to get up to even 1 volt.
IGBTs also have lower conduction losses at higher voltages. You will find IGBTs fitted in all high dc voltage grid tie inverters.
Mosfets are vastly better at lower voltages, and is what you will find in typical low voltage inverters.
Things like modern welders, and plasma cutters, use IGBTs as well.
I decided to run IGBTs in my Warpverter as its the logical choice for 100v operation. Very large old and slow IGBTs rated at hundreds of amps are not expensive, especially the Chinese clones, and the big IGBT power blocks are very compact and easy to bolt onto busbars and heavy lugs. Overload surge capacity of these big IGBTs is crazy high.
The 200 amp IGBTs I am using are rated to carry 1,000 amps of fault current for one full half mains cycle.
That is why my Warpverter has no electronic overcurrent protection.
Just a standard thermal/magnetic circuit breaker on the ac output.
Any dc current surge to trip the output breaker comes mostly from the electrolytics.
I have a two pole 63 amp dc breaker on the input, but in over six years of operation I have never tripped that.
Its always the ac breaker that opens.
Its seen quite a bit of unintended abuse over the years, and its never missed a beat in all that time.
This all works so well at 100v, I would not be surprised if similar large IGBTs would also be very successful at 48v.
While large IGBTs do drop a lot of voltage at full rated current, they are surprisingly efficient at much less than full rated current.
As domestic inverters generally run at low average power, with only occasional high peaks, I believe suitably oversized IGBTs might be brilliant in a 48v Warpverter.
In fact Alston over at The Back Shed is putting together a 48v Warpverter using large IGBTs right now.
Its now in the very final stages of completion, and I can hardly wait to see the results.
A very short thread with lots of pictures:
https://www.thebackshed.com/forum/ViewTopic.php?FID=4&TID=15183
Alston is using Klaus's control board, which I would highly recommend.
Klaus's board is identical to mine in every respect, but he has added the Hall effect feed forward load compensation modification.
My inverter has excellent line regulation, but load droops about ten volts at 5Kw, something that is not really a problem here.
The Hall sensor load compensation feature can be tweaked to have both excellent line and load regulation.
It can even be adjusted so that the load voltage increases slightly with increasing load, if you wished to do that, and its guaranteed 100% stable.