We had a brief power outage two nights ago, on the coldest night of the year. Temperatures got down to 5 deg-F, with a wind chill of -5! My DIY battery system combined with my Enphase IQ Battery 3T worked great!
Yes, and our fear was that the outage would last all night and my IQ Battery 3T would only last about 2-1/2 hours with the heater running. We only have electric heat here. The DIY battery setup allowed me to run the Enphase battery at only 200W so that it could last all night.You mean:
Your Enphase IQ battery 3T generated the micro grid and your AC coupled DIY hoymiles inverters (powered by batteries) helped.
Yes, and our fear was that the outage would last all night and my IQ Battery 3T would only last about 2-1/2 hours with the heater running. We only have electric heat here. The DIY battery setup allowed me to run the Enphase battery at only 200W so that it could last all night.
Probably, but I fell for Enphase and already had it in place. However, there are not many choices for UL 1741 "SA" qualified off-grid inverters that can do Freq/Watt control of the output. The new EG4 Hybrid says it is, so I would like to try this with one of those, but I can't afford one right now. I don't have enough subscribers to source it yet.It's great that your ad-hoc AC battery worked but it really seems like a different solution without iQ battery would have been simpler/cheaper.
Which one do you want? Maybe signature solar will sponsor you by sending you one to test out because obviously if you can make it work they will make them sell.Probably, but I fell for Enphase and already had it in place. However, there are not many choices for UL 1741 "SA" qualified off-grid inverters that can do Freq/Watt control of the output. The new EG4 Hybrid says it is, so I would like to try this with one of those, but I can't afford one right now. I don't have enough subscribers to source it yet.
The new Hybrid 8kW hybrid is the only one that might work because it is 1741 "SA" certified. The 6kW doesn't say one way or the other.Which one do you want? Maybe signature solar will sponsor you by sending you one to test out because obviously if you can make it work they will make them sell.
What is ‘SA’ and why might one want it?The new Hybrid 8kW hybrid is the only one that might work because it is 1741 "SA" certified. The 6kW doesn't say one way or the other.
UL1741SA has the specifications included for Freq/Watt and Volt/Watt control, that 1741 didn't have.What is ‘SA’ and why might one want it?
These say: ‘Globally certified for UL1741, SAA[/b{, TUV, VDE-AR-N 4105, VDE 0126, G83/2, CEL 021, IEC61727, EN50438, ABNT NBR 6149/16150’
Is that the same thing?
So 1741SA is just basic throttling of output through frequency shift (or voltage shift)?UL1741SA has the specifications included for Freq/Watt and Volt/Watt control, that 1741 didn't have.
Ahhh, gotcha. I though you were referring to the Microinverters themselves, not the hybrid inverters that can control them for backup power when the grid is down.You're missing the point. Grid-tied inverters have UL1741SA. Off-grid inverters mostly don't have UL1741 at all, or only have UL1741 without the SA, because they are not grid-tied. The new EG4 8kW is the ONLY one I've seen that is both, outside of Tesla, Enphase, & Generac.
Congrats!!.. I too got certified a few months back. They reviewed and approved my design within two days so you should be hearing from then soon
Look like you have to be an installer to register for Enphase University - hoq can I get certify without doing one?
One more subtle way for Enphase to sell more batteries.Yup. I received approval and final certification this morning. Yay!
I also learned that they use an inaccurate rule of thumb regarding NEC 2017, 710.15(A). They said regarding my SLD that the ESS must provide less than or equal to the largest circuit breaker in the backup sub-panel. That is not what the code says. The code says, that the capacity of the ESS "...shall be equal to or greater than the load posed by the largest single utilization equipment connected to the system." It is clear throughout the code book that "utilization equipment" is referring to the actual loads themselves and not the size of the circuit breakers in the panel. Clearly, such a restriction would be unreasonable considering Eaton, SQD, GE do not make AFCI breakers of values less than 15A, or breakers less than 10A in general. The wiring must be sized appropriately for the breaker, but the breaker value is not what NEC 710.15 is looking for. They almost had me convinced I was screwed using an IQ Battery 3T, because I can't get 6A breakers! Thankfully, I verified exactly what the code says and I'm good with my breaker ratings as long as my loads don't pull more than 5.33A continuous, or 6.33 surge at 240V.
Yes, that's close. I have the CT on the Grid input to my main panel to cap at zero-export for the HM inverters. I also have a relay where you have the CT, to turn off the inverter, and I have my current controller between the battery and the inverter that also controls the relay, low battery shutdown, and normal battery restart.
Is that smaller PCB on lower right your current controller?
Interested to understand whether those December 2022 final production samples actually ended up being final as well as any schematic or drawing you might have that you can share of how your whole rig is wired up…I'll be din-rail mounting the current controllers next to those 10A DC breakers. There is a 15A battery charger sitting in the bottom, that has no mounting brackets or available screw holes to mount it. Above that are my two battery banks, about ~7.5kWh. I'm waiting on the final production sample to arrive next week and 6 x HM-350NT inverters. I should have the whole thing assembled and hooked up in my garage in a week or two.
1. What I learned recently is, the monitoring doesn't work with the Dual and Quad inverters when all the Neg DC inputs are ganged together at the battery, because they are already internally ganged together inside the Dual microinverter. Due to this, the return current is not equally shared and takes the path of least resistance, causing errors in the current and power measurements as shown on the software. This does not happen when I was running two single microinverters, so I ordered all single HM-350NTs to use on this. That solves the problem.
2. Next I have some HMS-2000 2kW Quad microinverters coming in that are going to be tested with 455W modules. I wish I had bigger modules to test them with. They can output up to 475W per quadrant, so the 455 should have no clipping at all.
View attachment 119840