That keeps the wire from overloading but the receptacle and appliance can still exceed. Imagine a power strip in the middle of the circuit, or even just a regular duplex receptacle. Easily sink 30A out of that.You have a 15A breaker (1800W at 120V), and you plug in this inverter for 700W (6A more).
You now have 21A available to power a coffee maker and hair dryer on the same circuit. But the wire can't handle it.
Would work if PV backfed from far end of a wire, just like how we land the PV breaker at far end of breaker panel busbar.
But you likely have no idea how the various outlets and lights in your house are daisy-chained together.
In places like the UK with receptacle fusing it would be safer, possibly eliminating this issue. This OCPD essentially acts like the load breakers in the middle of the panel.
TBH this discussion needs to address how to safely backfeed to arbitrary branch circuits, there has only been 10% of the discussion spent on this…