An AC breaker can't handle that arc. A DC breaker can. At least that's my understanding.
Why is the fault current smaller along the 3 amp circuit?if the 3 amp fuse is protecting a small wire, then a short somewhere along that wire isn't going to be subject to the same available fault current at the battery terminals.
I may have stepped in it earlier today when my answer to someone with a (somewhat) similar question was that there were two wires, so two fuses. The fuse protects the wire for that segment. If the device cannot be expected to exceed 10 amps, then a 10 amp fuse is appropriate. However, if I'm understanding the "rules" right, we would be looking at no more amps on the wire than 80% of the fuse rating.
Why is the fault current smaller along the 3 amp circuit?
View attachment 39333
The only explanation for the fault current being smaller is that the circuit resistance is higher. Even when I consider the resistance of smaller wires I can't explain why the fault current would be that much less than at the battery. @smoothJoey's story makes me think the fault current is still pretty high on the smaller fuses.....and I am re-thinking a lot of things I have done for fusing in the past.
Now I’m fantasizing about a gigavac contactor (2W idle) per pack. T-class fuse on each pack positive. 500A shunt per pack. Want software defined fuse function shunt+contactor too. So much added cost.
Actually as I think about this ... the branch circuits won't be exposed to any more than the upstream fuse rating (at least not for more than the time it takes for the upstream fuse to blow). The available fault current on the branch is equal to the upstream fuse rating, no?
I went ahead and ordered a 3 amp ceramic fuse & holder with 10kA @125VDC rating (from McMaster-Carr) before I realized this. It's probably not necessary but it's designed to blow more safely than a glass fuse and since it's on the plywood at the battery, I'd rather not start a fire with a cheap fuse.
The interesting thing about this dialog is that there does not seem to be a defined method for figuring this out. (We may be DIYers, but I have found that on this forum, there is usually someone that has at least some of the science behind what is going on and how to do it correctly.)
We have a lot of good information on the properties of DC fuses and DC breakers.... but not much about how to design them into a system. I find this surprising. When it comes to safety devices, there is usually a lot of science and facts available that will guide a design.
The good news is that if this was a big problem.... we would be hearing about it. There are a lot of Marine and RV DC distribution boxes that use tiny automotive fuses and a lot of people installing LiFePO4. If it was a big problem we would be hearing about it. This is not to say we don't need to figure this out and find the best practices.... but it does mean the problem is probably not as big as we could imagine.
It's hard to say. I know the marine community is seeing an acceleration of the movement to LiFePO4. The number of installations are growing rapidly..... but a lot of them are using drop-ins like Battle-Born. I wonder what the fault current is at the battle-born terminals? Is the problem set any different for them?I suspect we haven't hit critical mass for the percentages involved in the failure scenarios to be relevant enough that we'd hear about it.
Interesting. My experience has been different. I have rarely found subjects about LiFePO and Solar from other sources that hasn't been covered on the forum to some level. Furthermore, there are profesional installers on the forum so we *do* get input from people that deal with this every day in many different installs.which (because I have soaked up a lot of information here) implies that this information is not making it to these forums.