Where do we start here? I've clearly explained the rationale for the decision. The 16K is EU 230V single phase, with the L=115V N=115V are HOT just like our 240V; WITHOUT A NEUTRAL for Split-phase . In my application, I will be using an external Neutral from the Autotransformer. The 16K firmware CANNOT operate in Split-phase and shutdown with F08 error. If there is an ARC fault error or Ground fault error, the 16K WILL NOT provide any protection as this happens outsides of its operating perimeter and hence I need a AFCI/GFCI combo breaker for NEC compliance.Since the inverter has internal AFCI/GFCI, why are you using an AFCI/GFCI breaker? Are you disabling the internal AFCI/GFCI?