I want to run my 240v us mini splits by themselves off grid,alone, what inverter did you use?My 240v only loads are
3x heat pumps
Water heater
Well pump
And a 5kw 230v inverter would run all my heat pumps
I want to run my 240v us mini splits by themselves off grid,alone, what inverter did you use?My 240v only loads are
3x heat pumps
Water heater
Well pump
And a 5kw 230v inverter would run all my heat pumps
I haven't installed yet but I bought mpp lv6048 for thisI want to run my 240v us mini splits by themselves off grid,alone, what inverter did you use?
Just double check, there are a few 240vac split-phase mini-splits that also use 120 vac to run their electronics power supply and relays like reversing valve. If it has a neutral wire connection it is a sign it also requires 120vac.I want to run my 240v us mini splits by themselves off grid,alone, what inverter did you use?
The mini splits I use are Mr cool and home Depot types and there wiring is l1 ,l2, G no neutral connection, I just don't know if l1 and l2 need to be 180 degrees opposite phase wave or if that even matters on minisplitsJust double check, there are a few 240vac split-phase mini-splits that also use 120 vac to run their electronics power supply and relays like reversing valve. If it has a neutral wire connection it is a sign it also requires 120vac.
It's single phase.The mini splits I use are Mr cool and home Depot types and there wiring is l1 ,l2, G no neutral connection, I just don't know if l1 and l2 need to be 180 degrees opposite phase wave or if that even matters on minisplits
I’m working on an off grid setup for electrical equipment that runs solely on 240v. From what I’ve garnered I would have the L and N from the EU 230vac inverter into a 240v circuit breaker and bond N and G at the main panel?I know of no air conditioners that use 120/240 volts. I saw some window units from the 60s that did, but I don't think that's what we're talking about here.
In an off grid setup, using a 230 volt L-N inverter and bonding the N to ground would work just fine for any 240 V-only appliances. But if you feed it with gride 240, you're most likely going to have a problem, depending on how the input connects to the output.
Yes, unless the N and G are bonded in the inverter. At any rate, you're going to have an odd ball system. You will have to use breakers with a "straight rating" of 240 volts. Your average run of the mill breaker has a rating of 120/240, which means that it is intended for use on a system with a maximum of 120 volts to ground. Your system will have a voltage of 240 to ground and therefore a standard breaker won't work.I’m working on an off grid setup for electrical equipment that runs solely on 240v. From what I’ve garnered I would have the L and N from the EU 230vac inverter into a 240v circuit breaker and bond N and G at the main panel?
I wonder if it’s better to do straight 240 or just use Euro-style breakers and consumer units.
Assuming using standard North America breakers… are you supposed to use single pole breakers?
There is no reason you couldn't use a double pole breaker and open the neutral with the hot. It just has to be a straight 240 volt breaker.On a breaker panel busbar, it would have to be single pole.
Many Square D QO breakers are only 120V per pole. The 2-pole 120/240V breakers are 120V per pole. The 3-pole breakers are all 277V, I think and some model number single pole and 2-pole breakers are.
DIN rail, many are. Like the Midnight CBI and Carling breakers. Some may have a Midnight sticker or web site listing that giving lower voltage, but the manufacturer sticker with part number and voltage is underneath.
There is no reason you couldn't use a double pole breaker and open the neutral with the hot. It just has to be a straight 240 volt breaker.
Right, that's what's called a straight rated breaker, a breaker with a 240 volt only rating. They exist, you just have to find them.If a double-pole breaker, it needs to be one where each pole individually is rated to 240V.
If you have 240V Line and 0V Neutral, two ganged 120V poles in series (one in Line, one in Neutral) will trip for an overload just fine.
However, if Line shorts to Ground (which is bonded to Neutral somewhere, only the pole on 240V line is available to break the arc. Because it is only rated for 120V (per pole), expect it to burn and fail to interrupt the arc.
If you are able to wire both 120V poles in series to interrupt Line, rather than having one open Neutral, then it would work.
So this wouldn’t work https://www.homedepot.com/p/Leviton...Volt-Thermal-Magnetic-R00-LB220-0TR/312392693Right, that's what's called a straight rated breaker, a breaker with a 240 volt only rating. They exist, you just have to find them.
Thanks for the information. Looks like Midnight Solar has great options.QO has them for 3-phase panels, which often carry 277V (Hmm, finding 240V not 277/480V). Same form factor as the split-phase panels. Schneider's website details ratings of the different models.
240V:
240V:
QOXD120 - Mini circuit breaker, QO, 20A, 1 pole, 240/415VAC, 3kA, plug in mount | Schneider Electric USA
Schneider Electric USA. QOXD120 - Mini circuit breaker, QO, 20A, 1 pole, 240/415VAC, 3kA, plug in mount.www.se.com
I think these were the Midnight breakers that said 120/240V but were actually CBI breakers rated 277V
These I think are from Carling and are sold by Midnight as 277V, but are only "supplementary protectors", which may mean they don't provide a full 1" of isolation between input and output, possibly other differences.
Testing Magnetic-Hydraulic circuit breakers
I've built myself a circuit breaker tester. I assembled three transformers into a 3-phase wye auto-transformer, and by means of a breaker and cord/plug it can be repurposed into a current multiplier. A breaker connects X1 to H2 and H3, providing 4.7x current boost on X2 paralleled with X3...diysolarforum.com
Thanks for the information. Looks like Midnight Solar has great options.
This would also be a straight 240v breaker?
100A, 240V AC, 60V DC, 1 Pole, DIN Rail Mount Miniature Circuit Breaker, Trip Curve: C, UL1077 https://a.co/d/aPSy950
Trying to also conceptually understand why someone would use a DIN rail vs main panel box?
Do DIN rails have current ratings like a main panel box?
Are there applications where one would prefer one over the other?
1) It would workIf I wanted an offgrid 240v breaker panel ONLY (in U.S.) for my two mini splits and well pump which are all two ungrounded conductors and a ground wire. In this example, the panel will be fed from a Victron EU 230/240v inverter and never connected to grid AC IN. 1) would this work and 2) where would the grounding take place?