You are welcome. I noticed I typed fast and make a mistakes on SSC it is supposed to be SCC. I typed too fast. Sorry for that confusion. I re-edit to fix that. Good luck.
It comes down to 26% tax credit and cents. You should spreadsheet it out on all the parts and costs. SMA required more parts to get to the same level as Sol-Ark.
If you plan to get the 24v battery, you will need to run the system at 24v for the SCC. Not sure which 20amp SCC you have, if you read the spec, I am sure it can do it. Make sure it can do 12v/24v. Could you list the SCC brand or spec to double check?
For example:
Two series(12v+12v=24v...
I want to see if I could combine (2) 1/0 awg wires in parallel and not using 4/0 wires. The reason is I have plenty of 1/0 awg copper wires and want to avoid buying 4/0 awg wires. I plan to use it in the 24v system with the EVE 280 batteries.
I see the 1/0 awg could handle it if you look at...
Another question, how many circuits are on the existing load center panel now? Are all those are critical loads? Could you turn off some when generator is running? I understand what you tried to do. Just need clarifications before I could draw a picture for you. Thanks.
What about an All-in-one for the remote monitor for the solar shed and equipment out in the elements? I am looking for an All-In-One PTZ camera that could be remotely controlled and has the temperature sensor, water leak and humidity alert notifications via email or phone calls.
I know you can...
Not sure which Sunnyboy you have. Some of the SMA inverters have an secure power outlet where you could use that when the grid is down. At least use that to power some loads.
But, all Grid-Tie inverters need the grid signal to work(thus, grid-tie) at either 240v/50/60hz depending where your...
Plan to max 167amp for a 24v @ 4000w system. (maybe max 200amp?) The manual recommend 4/0 awg wires for the DC battery bank and over current device protections. Also plan to use two BMSs for two 24v 8 cells banks (2P8S). I only have one BMS 24v 100amp so far due to the shortage. So, I plan...
The ForestAir unit is not a high SEER rated unit. It only has 8.8 SEER. No better than the windows air conditioner. The mini-split is just more efficient on running. Plus his Everlander has no windows like he first said in the video. Less heat from the sun. Good insulation.
In that case, get a battery insulated box to keep it warm. Hope where the wood cabin is located will shielded some of the colds. Or even put a blanket over the battery box to help on the self-discharging.
Similar questions and answers from another post about mini-splits in an RV. Always a trade off with designs and engineering.
https://diysolarforum.com/threads/powering-a-mint-split-unit-in-an-rv-by-solar-and-lithium-batteries.9803/post-107243
I see you got the SMA SI6048. That one doesn't have the secure power outlet when power goes out. It will required a battery to feed it. You will need the same model if you want to use it at 240v split phase, or use an auto transformer to make 120v to 240v.
The Sunnyboy will be able to...
For the micro-inverters to work OFF-Grid applications, like a micro-grid, you would need a battery-less expensive inverters like Sol-Ark, Sunnyboy with Secure Power Supply or Outback Skybox to have run in offgrid application.
Why not get the cheap MPP PIP inverters that could do batteryless...
Is it code compliance to run both AC @ 240V and DC @ 200V in the same conduit?
I had wires ran long ago that planned for AC generators along with live 240VAC wires for air conditioners, but never used the spare wires. Only the air conditioner wires are live. I plan to use the spare wires in...
Do you need both DC Circuit Breaker and T-Fuse? From the Mangum manual (below), it sounds like you can get away with the DC Breaker with Overcurrent protection device. Could someone confirm? T-Fuse are hard to find these days.
"
For safety and to comply with electrical code regulations, you...
Victron, you can use Raspberry pi to install their open source control panel and it will work if you want to save a few bucks.
Best to let @SolarQueen guide you since they have a warehouse in PR post Maria. I have emailed them in the past with questions on the products.
It comes down to...
Hi,
New here. I need help with a BMS recommendation for an odd 14S lifepo4 battery with at least 100a for a 48v system. I know 16S is ideal, but my inverter could take the low 36v and 64vdc. It is not in the sweet spot of 16S, but I believed the 14S would do for the range of 46.2v to 38vdc...
It comes down to panel being shaded or not. Total powers will be the same.
2P2S : A(1+2) B(3+4) Parallel AB
The above case, any shades on 1 and 2, the output be to the lowest current of the shaded panel. Thus, lower power for the string.
2S2P: A( 1 2 Parallel) B(3 4 Parallel) Series AB...
You need to be code compliance to feed to the grid. This vendor PluginSolar does the 120v for N.A. with their micro inverters. https://www.amazon.com/dp/B008AQS4AY/ref=as_sl_pc_ss_til?tag=pluginsolar-20&linkCode=w00&linkId=HOKO2HCRSOOJ5ACJ&creativeASIN=B008AQS4AY
I haven't see any 120v micro...
It will work. The main concern is continuous load. UPS typical rated 20mins time when running at full load. For example, if the UPS rated 1000VA, the wattage could be like 800W rated in real world usage for 20 mins. Plus the transformer and MOSFETs might not be able to power the device due...
There are RV videos that people installed them and use DC battery power with generator for power assist. It looks like the newer model is pure DC.
Here is the older 2015 video of Engineer775 did the install and test their hybrid model at a house.
3 x 325W panels and 90 Watt of AC power...
Here is the similar question was asked and answered on grid-tie, the diagram will give you how the grid and generator would work, as stated in the earlier posts, you can do manual or auto transfer switch:
Magnum diagram...
I just wrote a reply to Grid-Tied solar with a much complicated diagrams with the link below:
https://diysolarforum.com/threads/ac-coupling-for-grid-tied-solar.3840/
If your looking for an off-grid solution, Will's blue print link has many diagrams...