All right, gonna keep plugging away at this till I understand what works and I very much appreciate your patience helping me figure this out. I revised the figures in the Daily Wattage Calculation chart to reflect as closely as can what the useage will be and the number has been revised down quite a bit. Responding as well as I can also to your questions with answers below. Please be patient, I’m 70 years old and although not quite as dumb as a stump I come close.
@Mattb4
You list a 6 gal heater running at 430w all day (as needed) for 10,320wh.
- This is a mini-tank water heater and pump which I only intend to run for showers for a few hours when I am there and then shut down. Revised my figures for the heater and pump in chart.
Your refrigerator seems high as my larger refrigerator is about 1500wh a day.
- sunshine_eggo noted the same and suggested a fridge that would run about 60 watts so I redid my numbers in the chart based on his suggestion
And your water pump seems off also.
- Specs listed for that pump are ECO-WORTHY Diaphragm Pump 110V 1.5 max amps
Plus you say that lights are 12v with no indication of how you get that.
- Corrected on chart.
@sunshine_eggo
If shading or partial shading is a concern, all bets are off.
- Full sun once it comes up till very late in afternoon. No trees or anything else blocking (except clouds of course). Should have mentioned I am in South Tennessee near Nashville.
Are you sure about the power? Most hot water heaters have at least a 1500W element.
- Specs on the web site state 1300W. Taking it for granted it is accurate.
4awg is a little excessive. 6awg would be under 3% drop.
- Already have the 4awg so it will probably be used. Have about a 60’ run from panels to controller.
You will need a generator and some way to charge the battery.
- Have 8,000 and 3,000 watt generators if needed. The 3,000 watt one resides there permanently.
With only 9600Wh of storage - 4800Wh usable, your battery is very undersized for your needs.
- Revised the figures to reflect more realistically what could be used each day. Still adding in a few things even though they might not be used (i.e. toaster and microwave (have gas stove) and table fan (depends on how hot it is).
10 panels - 5 pairs wired in series. This does not make sense when you consider your combiner box. Do you mean 2S5P? Five groups of 2 panels wires in series with each of those groups in parallel? I would likely choose 5S2P for 100Vmp and 10A Imp (rounded). 10awg would result in a 1.2% drop.
- Yep, you done lost me there. I was under the impression that I could wire each pair of panels (5 total) in series and connect each pair to one of the strings in the combiner box and run the 4awg wire from there to the controller??? Is there a better way to set up the panels? If I have a 24v system nominal PV power for my charge controller is 2,000W per below and other stats if that helps.
Thanks again!!!