But it doesn't actually do that. Pulling the inverter grid disconnect leaves the critical panel running off the inverter batteries, leaves the batteries energized, leaves the PV array attached an operating. As far as the inverter is concerned, it looks like a grid failure, nothing more, so it takes over powering the critical panel. Removal of the meter shuts down AC back feed, so the disconnect doesn't need to do that, either. It feels like some sort of residual requirement that doesn't actually do the job intended here.The purpose of the disconnect on the outside of the house is so fire fighters can shut off all the power going to a house in case of fire.
The 18KPV manual makes it clear the RSD shuts off AC power generation by the inverter, shuts down the batteries, and makes the PV array voltage under 30 volts.
On that last note, how does it make the PV array voltage under 30 volts? The only thing I think it could do it short across the leads. Is that what it does? But then, if someone uses the disconnect for the PV DC leads, the arrays are now back to their open circuit voltage. Or does the PV DC disconnect also short the leads?