Best Sol-Ark 15 Battery?

Let's say that more wiring increase the risk of having a fire. Lots of electrical fires. Many are localized, and only damage the immediate area.

If you put two racks side-by-side, the risk is that one rack will start the adjacent rack on fire. Remember that NEC code is based upon LI, not LiFePO4. LI is notoriously hard to put out, and you just made it twice as hard. Plus you have twice as much fuel to light the entire house in a fire.

The 3 feet rule is to keep the other rack safe (assuming that it too is UL9540, and has some fire resistance).
You are overlooking this: “No more than 40kWh in any one location. Location being: 1) Inside house; 2) Garage; 3) outside house.”

40KWH is ok for grid tied. It’s ok for off grid should the sun always shine and/or want to live like a pauper. It’s not ok if you want normal amenities and/or have a shop.
 
You are overlooking this: “No more than 40kWh in any one location. Location being: 1) Inside house; 2) Garage; 3) outside house.”

40KWH is ok for grid tied. It’s ok for off grid should the sun always shine and/or want to live like a pauper. It’s not ok if you want normal amenities and/or have a shop.
I'd rather have one rack of 15kwh on fire than two racks of 15kwh on fire, or even one rack of 20kwh.

The 3 locations give you the ability to have 120kWh installed at one house, or 92 kWh if you limit yourself to racks of 15kWh. You could literally have them all within 10 feet of each other: 40kWh inside the house at a corner next to the garage, 40kWh outside the house on the other side of the wall from the inside 40kWh, and 40kWh in the garage, on the other side of the wall from inside the house. I'm not saying that is ideal, but not prohibited.

UL also gives you the option to have your specific setup tested that does not meet the UL 9540 safe harbor.
 
Last edited:
I'd rather have one rack of 15kwh on fire than two racks of 15kwh on fire, or even one rack of 20kwh.

The 3 locations give you the ability to have 120kWh installed at one house, or 92 kWh if you limit yourself to racks of 15kWh
And I’d rather have my 12x12 power shed on fire than my 48x36 finished shop, my moms house, or other outbuildings.

I will have around 135 KWH when I finish my build. Am I supposed to have four different climate controlled power sheds? The NEC go can f&@k itself. Quite literally as I am in Missouri.
 
No love for the EG4 PowerPro?
I'll give it some love. Just installed one of two - next one will go up this week. Very straight forward with the SolArk 15. Also can be mounted outside. It is heavy but the total cost is comparable to building your own rack mounted once you add in cabling etc. Easy comms with Sol-Ark (although it is not officially listed on the Sol-Ark battery list - Sol-Ark claims to be battery agnostic and it worked on first hook-up)
 

Attachments

  • 8D466E0A-2950-475E-AD8F-E6F879077D6C.jpeg
    8D466E0A-2950-475E-AD8F-E6F879077D6C.jpeg
    208.6 KB · Views: 20
  • B5015322-237C-4161-B30F-16468C26D024.jpeg
    B5015322-237C-4161-B30F-16468C26D024.jpeg
    222.7 KB · Views: 20
  • D4AAD2BF-1C13-473D-8FB2-CDE4C632EE12.jpeg
    D4AAD2BF-1C13-473D-8FB2-CDE4C632EE12.jpeg
    193.7 KB · Views: 20
No battery wires? This is the new "wireless" version?

The battery wires coming out the top didn't seem like a good idea for weather resistance.

Your pictures look like you hunted it down, hung it to butcher it, and mounted it on the wall.

Mike C.
LOL - You haven't heard of the invisible 2/0 cables? Pic taken before final completion. The EG4 Power Pro came with some cables but they were too short - designed to work with their EG4 18 Inverter mounted right above it. I live in the woods - we butcher whatever walks through that looks tasty :). I agree that the wires coming out of the top don't sound like the greatest idea. It is, supposedly, outdoor rated and they are amphenol connectors at the battery. Nonetheless Ill probably build a little shed roof over it and/or add a raceway.
 
I currently debating batteries to pair with my upcoming Sol-Ark 15k. As much as I like the Pytes stuff, I'm struggling with the fact that the PowerPro seems to be almost double the energy density (volume, not weight) of the various Pytes enclosures.
One thing to consider is that Sol-Ark doesn't currently support closed loop communication with the EG-4 PowerPro. I learned that a bit late as they advertise the Sol-Ark 15 Limitless as "battery agnostic". I initially programmed it to "BMS Lithium" code 00 on the Sol-Ark and it seemed fine, but when I emailed Sol-Ark they said it wasn't approved and to un-select Lithium and just use Batt %.
 
One thing to consider is that Sol-Ark doesn't currently support closed loop communication with the EG-4 PowerPro. I learned that a bit late as they advertise the Sol-Ark 15 Limitless as "battery agnostic". I initially programmed it to "BMS Lithium" code 00 on the Sol-Ark and it seemed fine, but when I emailed Sol-Ark they said it wasn't approved and to un-select Lithium and just use Batt %.
A number of people have reported unpredictable behavior using % without comms. Without comms you may need to use V and not %. YMMV.
 
Last edited:
I recently installed a 15k and went with 6x Ruixu batteries. Comms worked right out of the box. Haven't had any issues so far.
The Ruixu rack is very nice, would definitely recommend.
I've been curious about the Ruixu batteries and the 15k as far as coms... you're having no issues at all? Are you off grid or still tied to the grid? If you are tied to the grid are you selling back excess energy when available?
 
I've been curious about the Ruixu batteries and the 15k as far as coms... you're having no issues at all? Are you off grid or still tied to the grid? If you are tied to the grid are you selling back excess energy when available?
No issues at all. Have been running for about 3 months now.
Grid tied, but not selling excess.

I'm using my excess to mine crypto.
 
My system consists of two Sol-Ark 15ks in parallel, with 3 EG4 Power Pro's, and 6 EG4 LLV2's shared to both inverters. So far everything is working great. Had to do about 3-4 deep cycles (80% depth of discharge minimum) to calibrate the BMS between all batteries
 

Attachments

  • Screen Shot 2024-03-15 at 1.40.50 PM.png
    Screen Shot 2024-03-15 at 1.40.50 PM.png
    1.9 MB · Views: 15
A number of people of reported unpredictable behavior using % without comms. Without comms you may need to use V and not %. YMMV.
@muaddib721 Nice install. Did you use the raceways EG4 sells and then custom run the cables over to the Sol-Ark 15? What battery setting did you use on the Sol-Ark? @Oldphile are you suggesting using the comms and the "Batt Lithium" option on the Sol-Ark. When I first set it up I did that and "battery type". 00. (Sol-Ark has published a list of their tested batteries and has a bunch of info but sadly doesn't have EG4)
 

Attachments

  • Battery-Communications-Integration-Guide-V3.1.pdf
    2.6 MB · Views: 7
@muaddib721 Nice install. Did you use the raceways EG4 sells and then custom run the cables over to the Sol-Ark 15? What battery setting did you use on the Sol-Ark? @Oldphile are you suggesting using the comms and the "Batt Lithium" option on the Sol-Ark. When I first set it up I did that and "battery type". 00. (Sol-Ark has published a list of their tested batteries and has a bunch of info but sadly doesn't have EG4)
Not suggesting that you use comms. I'm suggesting that you use voltage and not %.
 
@muaddib721 Nice install. Did you use the raceways EG4 sells and then custom run the cables over to the Sol-Ark 15? What battery setting did you use on the Sol-Ark? @Oldphile are you suggesting using the comms and the "Batt Lithium" option on the Sol-Ark. When I first set it up I did that and "battery type". 00. (Sol-Ark has published a list of their tested batteries and has a bunch of info but sadly doesn't have EG4)
Battery type is 00... and yes as you can see in the pic i have the EG4 conduit boxes on top of each battery and then I ran connections to a main bus bar in the wiring trough below the two sol-arks, and then connected the main battery bus bar to the two sol-arks. I've been tracking deep cycle runs with all my batteries and here is the second and third cycle data. Also cycle 4 so far
 

Attachments

  • cycle 2.png
    cycle 2.png
    469.8 KB · Views: 6
  • cycle 3.png
    cycle 3.png
    565.2 KB · Views: 6
  • Cycle 4 so far.png
    Cycle 4 so far.png
    345.8 KB · Views: 6
Battery type is 00... and yes as you can see in the pic i have the EG4 conduit boxes on top of each battery and then I ran connections to a main bus bar in the wiring trough below the two sol-arks, and then connected the main battery bus bar to the two sol-arks. I've been tracking deep cycle runs with all my batteries and here is the second and third cycle data. Also cycle 4 so far
Wow, nice data. Thanks for posting.
 
FYI I am using 8 Pytes batteries and cabinets from stackrackbattery.com

Both batteries and cabinets meet all UL codes and are for indoor and outdoor installation in California too. I have no problems connected to Sol-Ark 15k.
 