Grounding a stand alone sub panel

As I understand it, it will disable the N/G bond completely. Otherwise, the relay will disable the N/G bond when the AC input is active. I haven't actually done this yet, so can't speak authoritatively. My system is currently so over provisioned I don't even think I need a generator.

I would think it disables it completely. My multipluss has the N/G bond but I now have a panel so I think I will N/G bond at the panel.

Do you happen to have a picture or wire diagram of your system? Wondering why you’d run a ground conductor from your panel to the bus, if,you already run a 3 wire from the multi to your panel. Your multi has a ground connection to,the bus as well?
 
Unfortunately I don't have an updated diagram handy. I'll try to explain in words.

I have 3 ground bus bars across my system:
  1. Outside in my MNPV6 combiner box. PV is bonded here and this bus bar is connected to a grounding plate.
  2. My DC panel ground bus bar is bonded to the outside ground bus via PV Teck 90 cable.
  3. The sub panel bus bar is bonded to the DC panel ground bus bar via the Multiplus AC Out 1 (the sub panel is connected to AC Out 1).
The Multiplus ground is connected to the DC panel ground bus bar.

I was planning on connecting my generator to the Multiplus AC In 1. The generator has a floating neutral. By disabling the N/G bond relay on the Multiplus and doing the N/G bond on the sub panel, I can always have the N/G bond on the sub panel regardless of whether the generator is running or not.

Does that make sense?
 