So, I've been putting all of my research to work and have everything "together"
I'm using 4x280ah eve cells with an overkill bms. Until yesterday these were at shipping capacity and sitting around 3.2v. These came from DLET off Alibaba.
For this initial assembly I'm just running a single < 5amp load with a fuse straight off the bms-/battery+ I have 800w solar going to a victron 150/70-tr on a breaker going to the bms-/battery+ I'm in the pnw, with a steep solar angle, and I'm half under a tree. Yesterday was fine and the setup ran all day in bulk. It generated 2.3kw, and this morning the battery was near full.
So I'm trying to set my charge controller and bms to reasonable yet safe settings. I dont need 100% from the battery, and I dont need 5000 cycles, I need a reliable battery that isnt pushing its limits.
I had my bms set at:
3.64 / cell over v
14.5 pack over v
I had the victron set at:
14.4 absorption
13.5 float
This morning when the sun came up, I was seeing about 30a going into the battery at 13.7v and one of the cells tripped the over voltage protection. It was about 0.2 over the other cells. I disconnected the charger and bumped the bms up to 3.65/14.6 and bumped the victron down to 14.1v.
The cells evened out and the bms protection came off. The batteries were probably only a couple of ah from where the were, since I dont have much load. The pack was at about 13.7v
Hooked everything back up and the charger went in to absorption but it was still putting about 30a into the battery, and a different cell tripped the over voltage protection.
So i disconnected the charger again and let the pack drain and even out. I bumped the absorption down to 13.6v and knocked the cell settings down a smidge on the bms for comfort.
Hooked it back up, and the charger was in absorption for about 30 seconds and went to float. I feel like this is a safe setting, but no where near what I have seen recommended around here. All of my cells are now within .002v of each other and it was a different cell that tripped both times. I know there isnt much capacity at the top either.
Do cells normally charge this unevenly at the top? Can anyone else with the same setup compare settings?
Are these reasonable settings?
I'm using 4x280ah eve cells with an overkill bms. Until yesterday these were at shipping capacity and sitting around 3.2v. These came from DLET off Alibaba.
For this initial assembly I'm just running a single < 5amp load with a fuse straight off the bms-/battery+ I have 800w solar going to a victron 150/70-tr on a breaker going to the bms-/battery+ I'm in the pnw, with a steep solar angle, and I'm half under a tree. Yesterday was fine and the setup ran all day in bulk. It generated 2.3kw, and this morning the battery was near full.
So I'm trying to set my charge controller and bms to reasonable yet safe settings. I dont need 100% from the battery, and I dont need 5000 cycles, I need a reliable battery that isnt pushing its limits.
I had my bms set at:
3.64 / cell over v
14.5 pack over v
I had the victron set at:
14.4 absorption
13.5 float
This morning when the sun came up, I was seeing about 30a going into the battery at 13.7v and one of the cells tripped the over voltage protection. It was about 0.2 over the other cells. I disconnected the charger and bumped the bms up to 3.65/14.6 and bumped the victron down to 14.1v.
The cells evened out and the bms protection came off. The batteries were probably only a couple of ah from where the were, since I dont have much load. The pack was at about 13.7v
Hooked everything back up and the charger went in to absorption but it was still putting about 30a into the battery, and a different cell tripped the over voltage protection.
So i disconnected the charger again and let the pack drain and even out. I bumped the absorption down to 13.6v and knocked the cell settings down a smidge on the bms for comfort.
Hooked it back up, and the charger was in absorption for about 30 seconds and went to float. I feel like this is a safe setting, but no where near what I have seen recommended around here. All of my cells are now within .002v of each other and it was a different cell that tripped both times. I know there isnt much capacity at the top either.
Do cells normally charge this unevenly at the top? Can anyone else with the same setup compare settings?
Are these reasonable settings?