It comes from the American Boat & Yacht Council (ABYC) standard for marine wiring. You will notice that it is a bit less conservative than the NEC. That is why I will often go up one size for selecting wire size.Where is this table from? NFPA? MTW wire?
Can you find & post the “Performance Specifications” for your already have 3 AGMs.
Battery Chemistry | AGM Valve Regulated Lead Acid (VRLA) |
Lead Calcium Grid Purity | 99.7% |
Nominal Voltage | 12V |
Nominal Capacity (C20 to 1.75V/cell) | 98Ah |
Cycles at 30% Depth of Discharge: | ~1500 |
Design Life on permanent float charge @ 25°C | Up to 10 Years (80% capacity retained) |
Charge Voltage @ 25°C | 14.1~14.4V (-4mV / °C / cell) |
Float Charge Voltage @ 25°C | 13.5~13.8V (-3mV / °C / cell) |
Recommended max Charge Current | 22.5A |
Internal Resistance: | ~6.5 mΩ (Fully charged) |
Maximum Discharge Current (5 Seconds): | 900A |
Self Discharge Rate | ≤3% per month |
Operating Temperature – Discharging | -20°C to +50°C |
Operating Temperature – Charging | -10°C to +40°C |
Operating Temperature – Storage | -20°C to +40°C |
Terminals | M8 Threaded with colour-coded Sealed Epoxy Blocks |
Max Terminal Torque | 5.5Nm (±5%) |
Hardware included | 2x M8 bolts 2x flat washers 2x spring washers |
Case Material | ABS |
Handle | Removable Polyester rope with plastic reinforcement |
Dimensions(mm): | 307mm(L) x 169mm(W) x 215mm(H) |
Weight(kg): | 24.5kg |
Here is an idea you might consider ,,, this is concept for you & I have not placed the fuses that would be required ,,, but a Blue Sea 4 Way Switch & eliminate your 2nd set of pos & neg bus;
Indeed. Thanks.it is the idea that counts
Thanks. I've made a copy to do later.Here is a spreadsheet
Yes I know... and it really is true. It chews power; 180W I believe. We tried it once for about 30 minutes just to see (before I knew it was 15A). In the design I put in a relay so it can only use 12V when there is power coming from the tow vehicle's alternator (which in turn would also be powering the DC-DC charger and thus supplying power to the whole system)I see you have a 3 way fridge. These don’t work well on solar/battery, they use too much electrical power. They are designed to run primarily on gas with AC when on unlimited shore power and 12V for when driving
Yes. I have considered installing a 2-way switch somewhat like you suggested so as to be able to charge the batteries both when the loads are either connected or entirely disconnected from the batteries. The problem being I haven't found one with a high enough current rating as yet; I really don't want to spend all the money up-sizing the wiring only to have the weak point be a single switch.
Indeed. Thanks.
Indeed. I'd want something at least 250A continuous. However, it's also AU$80! ?So the 4 Position “Blue Sea” Switch I posted earlier can take;
2,000 amps for 10 seconds
1,000 amps for 60 seconds
600 amps for 5 minutes
350 amps for “Ever” Or Continuous
It will be fine for your application.
The manufacturer actually sells a kit with the same inverter, same MPPT and solar "blanket" and a single 98Ahr battery.I think your biggest draw will be your 1500W Inverter & that will take about 150amps. You are planning on installing the 2 new batteries only. If that is the case & my 30amp per battery is a correct guess then you will have 60 amps available & need 150 amps. You can see, this is not going to work for the inverter.
Oh. I've no doubt that they're completely shit. All of their stuff is; it's all the same brand of cheap junk..... this is the part where I point out I wasn't the one who actually bought any of this stuff, and if it were up to me I certainly wouldn't have.In Short; I do not believe your batteries “will make the grade”.
It's a very long and wet drive to get to Arizona from here.I do not think you intend to hang out in Arizona
This is the first time I've ever heard about C-rating. ?The C20 capacity rating is 98 Ahrs ,,, what that means is if you drained your battery from 100% SOC “State Of Charge” to 0% in 20 hours you would get 98Ahrs total ,,, divide that by 20 hours = or 4.9amps for 20 hours. That is C20
Ha ha. Thanks. I did it using Google Drawings. Mind you it took me ages, mainly due to procrastination and a lot of unnecessary fiddling with hidden shapes to allow me to move things around and allowing the curved connector lines wires to move on their own.What did you use to create your diagram? That is amazing. I was about to post something and I am embarassed to post it now
I don't mind fudge factors, but i usually like to know what's behind the curtain.Take a look at the devices/appliances you will be running off your inverter & that with a multiplier (if unknown I would use 25%) for efficiency etc will get you what the Inverter theoretically will pull out if your battery bank.
400W / .85 / 10V = 47A (pretty similar to your results)Example, 400W device multiply by 1.25 = 500W ,,, 500W divide by 12 volts = 42 amps.
As typically the highest wattage draw in a system inverters that have programmable cut off points are invaluable for preventing undue stress on the various components.Many 12V inverters cutoff at 10V so...
I've never owned an inverter that can be configured. It will be high on my list next time. Which inverter do you have?I’ve set mine to cut off at the top of my battery’s discharge curve knee.
I don't mind fudge factors, but i usually like to know what's behind the curtain.
What I've learned on this forum is that to quantify this fudge factor, folks also look at the cutoff voltage of the inverter. Many 12V inverters cutoff at 10V so...
1500W / .85 efficiency / 10V = 176A
Obviously if your inverter has a different efficiency or cutoff voltage, those numbers should be used.
Similarly:
400W / .85 / 10V = 47A (pretty similar to your results)