Megarevo 8K Firmware Update

View attachment 156605 hello everyone. I am new to this forum. But I just spoke to MegaRevo today and I was having an issue with one of my inverters. They sent me the latest firmware. I have a website of my own and I can upload it to a Backpage if it is wanted by others?
Looks like you're on v23 (I just loaded v22 to get advanced menus working. (Supposedly there's an issue with Generator /AC Coupling feature on v22)

What were the issues you were having and what was supposed to be fixed with v23?

@fromport seems to be keeping track of them here.
 
Last edited:
Looks like you're on v23 (I just loaded v22 to get advanced menus working. (Supposedly there's an issue with Generator /AC Coupling feature on v22)

What were the issues you were having and what was supposed to be fixed with v23?

@fromport seems to be keeping track of them here.
It's not that I was having any specific issues. All of a sudden everything stopped working on one of my two inverters. Apparently an engineer from MegaRevo tried to do a firmware upgrade and it crashed. So I asked them for the files and I did it myself. That is how I came about having these files.

So I really can't tell you what has changed from one to the other.
 
It's not that I was having any specific issues. All of a sudden everything stopped working on one of my two inverters. Apparently an engineer from MegaRevo tried to do a firmware upgrade and it crashed. So I asked them for the files and I did it myself. That is how I came about having these files.

So I really can't tell you what has changed from one to the other.
Thank you for the new version, much appreciated.
I added it to my collection at https://www.dth.net/solar/megarevo/firmware/20230605/
Arm version is dated 20230613
DSP version is dated 20230605

I am considering updating one of my units to this new version coming weekend.
 
I have a problem if someone can guide me, I have installed 2 units to my uncle it turns out that the seller performed a remote update and it failed, they sent me the firmware version 2023 but one of the units was doing a kind of loop restarting continuously and therefore does not allow to install the update, is there a way to uninstall the failed update and install new data?
 

Attachments

  • Screenshot_20230711-074401.png
    Screenshot_20230711-074401.png
    288.4 KB · Views: 20
  • Screenshot_20230711-074415.png
    Screenshot_20230711-074415.png
    327.8 KB · Views: 17
  • Screenshot_20230711-074418.png
    Screenshot_20230711-074418.png
    337.5 KB · Views: 16
  • Screenshot_20230711-074427.png
    Screenshot_20230711-074427.png
    308.4 KB · Views: 18
  • Screenshot_20230711-074434.png
    Screenshot_20230711-074434.png
    350 KB · Views: 20
I have a problem if someone can guide me, I have installed 2 units to my uncle it turns out that the seller performed a remote update and it failed, they sent me the firmware version 2023 but one of the units was doing a kind of loop restarting continuously and therefore does not allow to install the update, is there a way to uninstall the failed update and install new data?
 
I updated to the latest firmware given above tonight. I am struggling with getting the Megarevo 8kW inverter to properly operate the "zero export to grid" feature, commonly referred to as "anti-reverse" or set through TOU settings in the "advanced settings > TOU > time 1-6 + grid charge/discharge config". I am currently only running a simple charge at night during Super Off Peak and Zero Export to Grid schedule during the day. No solar for this test system.

If anyone has successfully accomplished this can you share your config?
A file shared with me from the distributor regarding the June firmware update for those who need instructions.
 

Attachments

  • 8KLNA-AdvancedMode-Instructions.pdf
    542.3 KB · Views: 22
I have (3) x Megarevo's brand new, open box for sale. 8KLNA models. Message me if you're interested. Preferably buyers in the SoCal region to cut down on shipping costs. $2k per.
 
If any of you have had any success in getting Megarevo's assistance in working out the non-working Zero Export capability please refer me to your contact there. I have tried all firmware version and all allowable combinations that are supposed to enable the zero export capability, but none of them works. The latest one has been running for the past week in advanced mode, but still it has exported to the grid over 8kwh. I contacted Megarevo's technical assistance last week, and about a day later got a WhatsApp message from them asking for the wifi dongle serial number. I replied a few hours later, giving Megarevo all information requested and even presenting photos and graphical data of the grid feedback.

Succinctly put, Megarevo never followed up on my request for help. This past Monday I got a call from a "Sales Director" from Megarevo named "Lavier" that happened to be in Puerto Rico looking for business opportunities. He said that he had received my lead from the technical line personnel. We met for close to 3 hours, and I shared much information on the Puerto Rico market. Ha represented that the techincal assistance personnel was working on the situation I presented. Since no response from the technical personnel was received, I contacted the "Sales Director" and he pointed out that he would follow up on them.

Earlier today, I sent the technical personnel a message that went unanswered and then contacted the "Sales Director". To my surprise, he advised that Megarevo would not honor the warranty of their manufactured inverters if they had not been purchased directly from them. In response to the exporting issue, he advised that whoever does not want to export to the grid should purchase an off-grid inverter. He went on and pointed out that Megarevo is certified by the local utility company, and then I advised that I would inform the local utility and the local Energy Commission of Megarevo's refusal to support their manufactured products on a clearly warrantied issue, and that Megarevo's refusal to warrant its products could result in their decertification. I advised that under the products liability laws all entities involved in the distribution chain from the manufacturer down was liable for the warranty, yet the "Sales Director" reiterated Megarevo's stance and refused to text with me anymore as he claimed that I was "scaring" him.

This is a most unfortunate situation, as until today, and excepting the non-working zero export function, I could only say good things about this inverter. I have been testing it under loads exceeding 8kw, even subjecting it to unbalanced inductive loads and it has performed better than expected.

Unless Megarevo comes clean, I will proceed and distribute inverters from manufacturers that are responsible and back their products. Too bad, since they were coming up with a split phase low voltage 12kw unit in September -at least that is what the "Sales Director" informed during our lengthy meeting-.
 
Last edited:
If any of you have had any success in getting Megarevo's assistance in working out the non-working Zero Export capability please refer me to your contact there. I have tried all firmware version and all allowable combinations that are supposed to enable the zero export capability, but none of them works. The latest one have been running for the past week is the June sw version in advance mode, but still I have exported some 8kwh. I contacted Megarevo's technical assistance last week, and after getting a WhatsApp message from them asking for the wifi dongle serial number. I replied a few hours later, giving Megarevo all information requested and even presenting photos and graphical data of the grid feedback.
Just for my own curiosity/learning, what values/data set are you looking at that show whether or not (and when) you're exporting to grid? (So I can keep an eye on dad's 8k unit)
 
Start with not relying on the Solarman App. While it does graphically show when the inverting is back feeding, and on earlier versions of the firmware it logged the amount exported, the newest version stopped logging the export power when you enable the zero-export function. I have a Shelley Pro3EM power meter connected right after the main breaker on the meter box where it logs both power coming in and the one that goes out. In average, the inverter is exporting a little over 1kwh per day. Apart from the risks of exporting when it is not supposed to, the concern is that without a net metering agreement one could be subject to penalties from the utility company and even civil fines, and to make matters worse if the meter is not set for net metering it reads the export as if it was import power coming in, thus you are billed 2x for the power fed back into the grid.

There are cheaper alternatives to the Shelly Pro3EM that might work as well in these circumstances. Just hook it up and you will if your system is exporting. Do note that the export is most common during the day, when consumption drops considerably to under 1kwh, at that time the inverter charges the battery to 100%, goes on to discharge it some 2% back to the grid and then recharges again. This is cycle that will be interrupted when consumption has sudden and considerable increase, as when the microwave, stove or a water pump starts to run.
 
So I have been in communication with Megarevo via WhatsApp this past week. I think... I think we have a solution for the zero export to ct's. The following was done and I am curious if it works for others:
1. Firmware Version: 1.4.13.BO3D27_20230605.out / LNAV23_20230613.axf
2. Make sure the CT clamped on L1 grid before distro panel (just pick a wire) is the same 120V leg that L1 going into inverter is. Same for L2. The tell here is if your inverter current output is at 0.4A or higher. If its just 0.4A-0.7A and your load is considerably larger, you likely need to plug CT1 into port 2 and CT2 into 1.
3. Sys Setting > Work Mode > Peak Shift
4. Sys Setting > Bat Wake Up > Disabled
5. In your TOU settings
5a. Advanced Settings > TOU 1 > Time > 12am - 6am (change as required) SOC Target 95%
5b. Advanced Settings > TOU 1 > Grid Charge > Enabled
5c. Advanced Settings > TOU 1 > Time > 6:01am - 23:59pm (change as required) SOC Target 35%
5d. Advanced Settings > TOU 1 > Grid Charge > Disabled
6. Advanced Settings > Working Mode > SFC Selldis > Select
 

Attachments

  • 20230716-RKLNA8K-Advanced-Setup.pdf
    542.3 KB · Views: 29
  • 20230716-RKLNA8k-Basic-Config.pdf
    348.6 KB · Views: 29
  • 20230716-Solarman-Readout.jpg
    20230716-Solarman-Readout.jpg
    113.1 KB · Views: 51
  • 20230716-RKLNA8K-Wiring-Diagram.jpg
    20230716-RKLNA8K-Wiring-Diagram.jpg
    160.6 KB · Views: 57
Last edited:
Thanks for the information. Yesterday morning some other Megarevo personnel contacted me after I posted their Sales Director's claim that they would not honor the warranty if it was not a direct purchase from Megarevo. The new contact apologized for the misunderstanding and it appears that they will address the issue.

It seems that not everyone within Megarevo was aware of the zero export issue, as I had to explain that this is a widespread problem that has been amply discussed in this and other forums. The technician that originally contacted me texted me afterwards and again apologized for the delay as he had been out of the office last week.

Hopefully the issue will be addressed and if all goes well resolved -perhaps with the solution shared by AnbroEnergy-. I insist, other than this issue, I have only had good results with the Megarevo units. I would prefer a simpler and more amicable UI and a more functional app, but those are concerns that can be resolved with the new color touchscreen and using Solar Assistant as it continues to integrate Megarevos' programming into its code.
 
Well the TOU instructions above did not work as intended. It appeared to be functioning correctly for the first 12 hours but after that it started to randomly discharge all the energy from the batteries back to the grid even though the settings are selected as "grid sell > disabled" and "grid charge > disabled" during those time periods. Perhaps this product works well as a solar inverter but the concept of zero export to grid hasn't been solved yet.
 
Well the TOU instructions above did not work as intended. It appeared to be functioning correctly for the first 12 hours but after that it started to randomly discharge all the energy from the batteries back to the grid even though the settings are selected as "grid sell > disabled" and "grid charge > disabled" during those time periods. Perhaps this product works well as a solar inverter but the concept of zero export to grid hasn't been solved yet.
That has been my issue from the beginning.
ToU is _unusable_ imo since instead of just covering the load, the fans go to full speed and put as much as it can generate back into the grid.
And I have been unsuccessful communicating this to MR.
 
That has been my issue from the beginning.
ToU is _unusable_ imo since instead of just covering the load, the fans go to full speed and put as much as it can generate back into the grid.
And I have been unsuccessful communicating this to MR.
Megarevo tried to throw it back on me saying the reason the "zero export to grid" is because I likely installed it incorrectly. And that was the end. A warning to those who are thinking of purchasing their equipment or white labelled versions of their equipment.
 
In my case I was contacted by Megarevo's after sales service and in sum they apologized for the misunderstanding that occurred, and assured that they do support their products irrespective whether they were purchased directly from them or through a reseller. A technician worked remotely on the inverter I am testing and adjusted its parameters. At the present time I don't know in detail the changes that were made, but the inverter has gone from exporting an average of 1.5kwh to 65w and 95w in the past couple of days. It is too early to conclude that the issue has been mostly solved, I will update you all once at least a week has gone by. I understand the few watts that register as exported are negligible, as they could be the result of many other factors, including emf or CT's inaccuracies. I will share with you the solution and suggest the Megarevo technician take part in this post.
 
@potin
Fyi... SigSolar was having a hard time when MR & the Zero Export issues apparently
CTs towards the grid. Like the manual says.
I went to Megarevo in China to talk to the engineers about all the problems we still have with the inverters and found out that the inverter can’t Zero Export.
... They said they can’t guarantee that the inverter wouldn’t sell back to the grid. I have been working with Megarevo for over a year now and have gotten nowhere with this company. We have changed our manual and spec sheet online since then to state this inverter does not Zero Export. ...

Fyi...
Here's my dad's 8k setup/issue summary I helped him with (& SigSolar & this thread).
- John4178/Mpgrimm2 EG4 8Kv Setup Post here and Grid Charge Issue here.

And here's what appears to be our working setup using the Advanced ToU settings & fw v22 ...
- John4178/Mpgrimm2 EG4 8kv working Setup fix 7/3/23 post

...maybe it will help you out?
.
 
Last edited:
It seems Megarevo has mostly dealt with the Zero Export issue. After a week of running the inverter with Megarevo's parameters the export has reduced form 8.14kwh per week to 909.94wh this past week. Again, the inverter shows 0 export in its logs and the measurements were taken with a Shelly Pro3em connected on the grid lines outside of the 50a breaker on the line feeding the inverter. I am still not discounting the existence of some power being fed back, but some of these readings may be the result of stray current or other events that can hardly be controlled.
 
I can't believe this grid feed problem is still happening after all this time. I got my unit Dec 2022 and left off the guessing in this forum the end of March. I see SS/EG4 are hot on their new 18k, which leaves us further in the dust!
What I've done to curtail the grid backfeed is to install a 40 amp contactor controlled by either a Kasa smartswitch for manual or scheduled Grid charging. If the SOC goes below 23 percent, I use the generator start relay contacts to trip the contactor for 2 hours at a time. This way I'm not at the Grids mercy for sucking up all my stored energy. Been there, lost a lot!!

My latest problem is the BMS comm faults I get every couple days since I had to change from the CAN protocol to RS485 to my EG4LP batteries.
Anyone dealing with that?
 
I can't believe this grid feed problem is still happening after all this time. I got my unit Dec 2022 and left off the guessing in this forum the end of March. I see SS/EG4 are hot on their new 18k, which leaves us further in the dust!
What I've done to curtail the grid backfeed is to install a 40 amp contactor controlled by either a Kasa smartswitch for manual or scheduled Grid charging. If the SOC goes below 23 percent, I use the generator start relay contacts to trip the contactor for 2 hours at a time. This way I'm not at the Grids mercy for sucking up all my stored energy. Been there, lost a lot!!

My latest problem is the BMS comm faults I get every couple days since I had to change from the CAN protocol to RS485 to my EG4LP batteries.
Anyone dealing with that?

Dad's EG4 8k setup is on fw v22 which seems to be working fairly well now. No apparent issues with the 6x EG4 LifePower4 battery comms on our end (RS485 direct to 8k inverter... Haven't update battery fw yet).

See 2 posts above for our setup.
 