The code says that your electrical system must have a grounding electrode. If it is a rod type electrode, it must have a resistance of 25 ohms or less. That means if you drive a single rod, you must have some means to verify it meets the 25 ohms or less requirement. It can't be done with a regular multimeter on the ohms setting.
BUT! The next paragraph or so in the code tells you that if you can't get 25 ohms or less, you can add an additional rod, at least 6 feet apart, and connect it to the first rod. There is no requirement to verify the ohms of the two-rod system. So you either find a way to do a complicated 3 point fall of potential earth resistance test... Or you can just add a second rod and be done.
So, let me make sure I have this straight..
Being as he is off grid / building his own new house.. he needs two rods or a fancy as* way of verifying the resistance of his single rod. All houses / buildings with their own separate electric connection to the grid or offgrid would need / normally have this setup I'm assuming. If a separate building is getting it's power from some other building, that has said rods somewhere in the circuit and the distance is appropriate, you would just ground back to the other building and not put in any more rods at that location.
2 legs good! 4 legs bad!