OK,
Here are the full specs of the panels.
View attachment 172648
for convenience here is the inverter spec again:
View attachment 172643
I am assuming 2 strings of 8 panels on Mppt1 1 string of 8 on MPPT2 and one string of 7 on MPPT3.
We already determined the Voc was not an issue. I won't rehash that.
Because these are bi-facial, we have to adjust Imp and Isc for the backside gain. They only give data for the smaller panel, but we can see that Isc and Imp increase proportionally to the power gain. (if the gain is 25% Isc goes up 25%).
Edit: Corrected my math. End result is the same.
Now we have to decide what to assume for backside gain. To be safe, we should assume the full 25% gain. Consequently, the Isc for the panel is 1.25 x 14A =
17.5
For MPPT 1 with two strings, that puts the array Isc at 2 x
17.5A =
38A THIS IS A RED FLAG because it is above the 31A limit!!!
For MPPT 2 and MPPT 3, the array Isc is 14A, under the 15A Limit.
I won't calculate Imp for this configuration because we know the configuration does not work.
Note: I calculated backward and a backside gain of only
11% will cause issues with 2 strings on MPPT1. It looks like these panels need to be limited to 1 string on all 3 MPPTs.
So what should we do? Let's look at 1 string of 10 panels on each of the 3 MPPTs.
We already know Isc is OK for a single string, but we have to recalculate Voc.
Voc will be 10 x 49.92V = 499.2V. That is just under the top of MPPT operating range and has over 20% headroom for the max voltage of 600V. That looks good so far but we need to look at the temp coefficient and cold temp gain.
View attachment 172644
With a low temp coefficient of -.26 and 20% headroom, it is doubtful there are any cold temp issues, but I looked it up in
this resource and found that the configuration is good to something well below 41F (40C). (That is as low as the charts in the resource go)
So,
1 string of 10 of the panels on each MPPT will work. Great! However, we need to check Imp to see if there will be any clipping. (Clipping means that the MPPT will not use as much power as the panels can produce).
Assuming an array backside gain of 25%, the Imp for each string will be 13.11 x 1.25 = 16.3875. This is well under the 25A usable current of MPPT 1, but it is above the 15A usable current of MPPT 2 & 3.
This means that if the panels are producing at 125% of their rating, MPPT1 and MPPT2 will only use 15A of the available 16.4A. Working backward, clipping won't happen till the panels are producing at 14.4% greater than the STD rating. Personally, I would not worry about it.
Note: There was a lot of math and I tried to show my work to help teach. If you have questions about any of it, please ask.
EDIT: added the following
One more observation. With no backside gain, the panels are at 30x550=16500W. With only 10% backside gain, it will be at 18K and the mpps will start limiting any further gain. 30 of these panels matches the inverter capability quite well.