WattAboutThat
New Member
- Joined
- Dec 15, 2021
- Messages
- 123
QUESTION OF THE DAY…
Setup:
2 x 18kPV Inverters
60 385W Canadian Solar Panels
wired as 6 strings of 10 panels each string
Intent:
To wire one string to each mppt
(not using parallel ability of mppt 1 for now)
intend to buy 20 more panels later to make
use of mppt 1 parallel
each mppt max is 15A at inverter
each string is about 11A from panels
(mppt 1 max paralleled is 25A)
QUESTIONS:
Question One (1):
Pros and Cons
of using a Watts247 4 string to 2 out combiner box
https://watts247.com/product/solar-panel-combiner-box-4-circuits-to-2/
is this box reliable?
i intend to use 2 strings per combiner box
one box will only get 1 string leaving
availability to add a fourth string in future
for mppt 1 paralleled port in inverter
no strings will be combined
the only intent it to get
fuse, breaker, spd, for each string
so i will not be using 2 of the pv inputs on each box
essentially it is a single string combiner
(even though not combining)
and 2 strings per box)
Please Advise?
Question Two (2):
The panels will be approximately 100 feet
or less from Solar Control Room with inverters.
I also intend to have IMO Disconnects.
Two strings per disconnect (one not used but reserved for mppt 1 parallel string later).
I am thinking to place the
IMO Disconnects out at the Panels,
and placing the Combiner Boxes
inside the Solar Control Room.
But I could reverse this
so combiners are at array
and IMOs are in control room.
I understand the combiners should be prior to wire run to protect wires, so therefore argument is to place at array, but my gut wants to put them in the control room.
What are the pros and cons I should consider
to avoid any or most issues, I may not be considering?
As always, your advice is greatly appreciated!
Setup:
2 x 18kPV Inverters
60 385W Canadian Solar Panels
wired as 6 strings of 10 panels each string
Intent:
To wire one string to each mppt
(not using parallel ability of mppt 1 for now)
intend to buy 20 more panels later to make
use of mppt 1 parallel
each mppt max is 15A at inverter
each string is about 11A from panels
(mppt 1 max paralleled is 25A)
QUESTIONS:
Question One (1):
Pros and Cons
of using a Watts247 4 string to 2 out combiner box
https://watts247.com/product/solar-panel-combiner-box-4-circuits-to-2/
is this box reliable?
i intend to use 2 strings per combiner box
one box will only get 1 string leaving
availability to add a fourth string in future
for mppt 1 paralleled port in inverter
no strings will be combined
the only intent it to get
fuse, breaker, spd, for each string
so i will not be using 2 of the pv inputs on each box
essentially it is a single string combiner
(even though not combining)
and 2 strings per box)
Please Advise?
Question Two (2):
The panels will be approximately 100 feet
or less from Solar Control Room with inverters.
I also intend to have IMO Disconnects.
Two strings per disconnect (one not used but reserved for mppt 1 parallel string later).
I am thinking to place the
IMO Disconnects out at the Panels,
and placing the Combiner Boxes
inside the Solar Control Room.
But I could reverse this
so combiners are at array
and IMOs are in control room.
I understand the combiners should be prior to wire run to protect wires, so therefore argument is to place at array, but my gut wants to put them in the control room.
What are the pros and cons I should consider
to avoid any or most issues, I may not be considering?
As always, your advice is greatly appreciated!