When looking at mount 2-1 the camera perspective and angle of the ground alters the perspective of the phono and our eye. That cross brace is in fact not horizontal and no triangle is formed. It's an optical distortion.
OK, not a rectangle. Horizontal or slope, it is still a parallelogram. It resists wind pressure, and earthquakes, based on the torsional strength of the pipes.
My recommendation is to change connections to top & bottom of uprights, so it is entirely
rectangles triangles.
Mount 3-1 left to right braces not required for wind loads in our locale. Mount design drawn by a solar engineer and permitted. Each concrete block weight is about 1100 pounds each. That's 6000 pounds of weight and the blocks are 24 x24 x 24 inches, about 10 inches into the ground to prevent sliding.
Maybe not for wind. Do you get earthquakes? My SWAG is 1g horizontally, and shaking repeatedly.
I have diagonal braces left/right.
Yes, those are Delta lightening arrestors. I also have them mounted to Midnite Solar combiner boxes. We get maybe 4 lightening events a year hear and that would be a lot. I know about the Midnite LED, but that simply is not a concern worth the hundreds extra in this locale. But if I was back in Florida, I sure would spend the extra on Midnite arrestors.
Have you looked at the voltage clamping curves published by Delta?
I have absolutely no reason to believe them. On a whim I tested mine, and found it held off 5000Vrms (about 7000Vpeak) without clamping.
I contacted Midnight, who's engineers are about the most respected and have been around the longest of anyone in the alternative energy industry. They just replied wryly, "Cut the end off and pour the sand out."
"Silicon Dioxide Varistor" my @$$!
Watch Midnight's videos. Absolutely nothing happened. Until cranked up to 50,000V, and then they blew apart.
I didn't want to spend the hundred fifty bucks either.
Some of my inverters have MOV installed on PV lines, but not all. I ordered more from Digikey.
For the AC side I was going to build one similar to Midnights, but ended up getting an unused industrial one for the same $150 price.
Surge arrestors are used on AC and DC side of PV inverters for protection, to clamp high voltage transients. One inverter I have (actually several) are in the SMA family SUNNY BOY 5000-US / 6000-US / 7000-US / 8000-US. These come with a kit of MOV to protect the DC side: The MOVs are about...
diysolarforum.com
All panels face south at 27 degree tilt. Remember, this was 2015-17 and nobody even knew much about net metering 2 let alone 3 and the changes. But yes, today, I would like a Southwest facing array too.
yeah, mine is aimed South West, was all one orientation. Based on time of use in 2003 (Noon to 6:00 PM.)
Now that peak is 4:00 to 9:00 PM, I've added about 33% more aimed almost due West.
Mount 13-1 green wire: So at each array is a 10 foot grounding rod. Connected to the grounding rod is solid copper bare wire #8 I believe. This wire travels from the grounding rod and is bonded with UL approved ground connectors to each panel. the panels and their connections ground out to the array galvanized pipe and cross pieces. The grounding wire then connects into the Midnite Solar Combiner box which contains a grounding buss bar. The bare wire then completes the loop back to the ground rod, all uninterrupted. The green wire you see is connected to the combiner box buss bar. so is the Delta lightening arrestor ground connector. From the combiner box (which contains Midnite Solar 15 amp fuses for each parallel string, travels the PV +, PV- and the THHN green ground wire into PVC conduit. All of the arrays converge at a Schneider electric DC disconnect switch. The PV+ sides are solar fused across the blade switch, the negative PV passes through and the box is also grounded with a buss bar. This travels into the load center where the ground wire terminates on a buss bar that is also connected to two 10 foot grounding rods at that location connected by bare copper wire into that ground buss. So five grounding rods, 3 at arrays, 2 at the load center and inverter. From the buss bar, the PV wire passes thorough another DC breaker to the charge controllers which accept input as PV+, PV- and ground and output to the batteries as PV + and PV-. It's a little hard to write out, but it works.
I understand a bunch of ground rods, but it wasn't clear to me the network of conductors for ground go all the way back to chassis of inverter (or SCC).
''where the ground wire terminates on a buss bar that is also connected to two 10 foot grounding rods at that location" makes it sound like it stops short of the inverter.
That is the primary thing I'm concerned with. Wire from inverter to PV panel frames ensures fault current, in the event of a short to PV frame, gets back to inverter without having to go through dirt (or people.) Also, some inverters drive AC onto PV+/-, and people have gotten shocks off the frames, until they completed the circuit with a wire.