Issue: VMP voltage is low.
System:
Grid tied single string using Sunny Boy 3.8kw us-41 inverter. Designed and installed diy. Finishing final steps before requesting inspection.
Location: Southern California
9 Solarever panels, each at 455w. Connected in series with APSMART single rapid shutdown devices one pet panel.
Tilted 23degrees facing south
From array to inverted: less than 15 ft, 10G wires
Inverter: sma Sunny boy 3.8 US41
From inverter to service panel : less than 10ft. 10G wire.
Module VMP: 41.51VDC
Expected PV Array VMP voltage 9x41.51:~370VDC. Actual: received at the inverter: 270-290VDC
Array max output expected: 3600w, actual at full sun: 2400w
Inverters AC output ~240V. ~9.5 AC Amp
Why my output is low? (Edit in March 2024, two Apamart devices were faulty)
Is 55 to 65% efficiency normal? (Edit in March 2024, No. )
Are APSMART shutdown devices the culprit? (Edit in March 2024, indeed they were the issue)
how to troubleshoot? ( Edit in March 2024, See this post)
Edit on 26March2024: Two APSmart devices were not functioning properly, bypassing two modules, this low voltage. See this post for details:
Post in thread '4kw system outputting 2.5kw. Why?'
https://diysolarforum.com/threads/4kw-system-outputting-2-5kw-why.62392/post-1048446)
Thank you in advance.
I've read @Hedges is the SME at SMA products.
Everyone, Please let me know what you think.
Details including pictures ere in a poat in thread 'Drafted my design- aiming a 4.5KW grid tie system'
here in a poat in thread 'Drafted my design- aiming a 4.5KW grid tie system' hre in a poat in thread 'Drafted my design- aiming a 4.5KW grid tie system'
https://diysolarforum.com/threads/drafted-my-design-aiming-a-4-5kw-grid-tie-system.53251/post-777357
.
System:
Grid tied single string using Sunny Boy 3.8kw us-41 inverter. Designed and installed diy. Finishing final steps before requesting inspection.
Location: Southern California
9 Solarever panels, each at 455w. Connected in series with APSMART single rapid shutdown devices one pet panel.
Tilted 23degrees facing south
From array to inverted: less than 15 ft, 10G wires
Inverter: sma Sunny boy 3.8 US41
From inverter to service panel : less than 10ft. 10G wire.
Module VMP: 41.51VDC
Expected PV Array VMP voltage 9x41.51:~370VDC. Actual: received at the inverter: 270-290VDC
Array max output expected: 3600w, actual at full sun: 2400w
Inverters AC output ~240V. ~9.5 AC Amp
Why my output is low? (Edit in March 2024, two Apamart devices were faulty)
Is 55 to 65% efficiency normal? (Edit in March 2024, No. )
Are APSMART shutdown devices the culprit? (Edit in March 2024, indeed they were the issue)
how to troubleshoot? ( Edit in March 2024, See this post)
Edit on 26March2024: Two APSmart devices were not functioning properly, bypassing two modules, this low voltage. See this post for details:
Post in thread '4kw system outputting 2.5kw. Why?'
https://diysolarforum.com/threads/4kw-system-outputting-2-5kw-why.62392/post-1048446)
Thank you in advance.
I've read @Hedges is the SME at SMA products.
Everyone, Please let me know what you think.