With 3 or more parallel panels, the current due to a short can become a hazard if the current from other strings back-feed into the shorted panel. Consequently,
an OCPD must be placed on each parallel panel or parallel string of series panels. The OCP devices must be rated for 156% or more of the Isc of the panels.
(Many panels have a ‘series fuse rating’. This is the *most* current the panel can handle without damage and therefore the OCPD current rating must be less
than this value. This value is usually quite high compared to Isc and therefor is not usually a factor.) The minimum Voltage rating of the OCPD must be the
Voc x Temp-factor of the of the combined voltage of the number of panels in series. (See page 3 for description of the Temp-factor )