When we built the original part of the system, we only bought 4 batteries and we were going to call it good but decided to double our investment so we could really be "comfortable" with all of our power. DOH! We pissed away all that money so the damn thing could power itself into the ground!
 
Thank you for that feedback. This is what the guy actually said to me:

"


Though I appreciated the information, I was dumbfounded at "it is not a major concern for this low consumption application". What he is saying is that I can run my system idle for 5 days before I run out of power... GREAT! Uh, except I'm supposed to be able to use that power, not put a bow on it and pat myself on the back for being able to generate and waste power!

I still say something is wrong.. Just went to Fortress website and found this:

How can a 48 volt 105 amp-hour battery with a 30 watt self draw be 99% efficient? It even says right in the spec sheet there are no fans and self discharge is less than 0.8% per month.

There's an easy way to solve this on your own.. Charge up your batteries and then disconnect one and put it on the shelf.. leave the battery in active mode. Record the voltage every 12 or 24 hours until it goes to the lowest voltage permissible. Then do some simple math.

Really, if that 30 watts is real, not only will you find that the case on the battery is warm to the touch just sitting there doing nothing, but the battery voltage will drop to empty within 7.5 days.. 30 watts x 24hrs = 720 watts x 7.5 days = 5.4kW. That's ridiculous, and I suspect a typo in the email and the guy didn't catch it.
 
I still say something is wrong.. Just went to Fortress website and found this:

How can a 48 volt 105 amp-hour battery with a 30 watt self draw be 99% efficient? It even says right in the spec sheet there are no fans and self discharge is less than 0.8% per month.

There's an easy way to solve this on your own.. Charge up your batteries and then disconnect one and put it on the shelf.. leave the battery in active mode. Record the voltage every 12 or 24 hours until it goes to the lowest voltage permissible. Then do some simple math.

Really, if that 30 watts is real, not only will you find that the case on the battery is warm to the touch just sitting there doing nothing, but the battery voltage will drop to empty within 7.5 days.. 30 watts x 24hrs = 720 watts x 7.5 days = 5.4kW. That's ridiculous, and I suspect a typo in the email and the guy didn't catch it.
Good idea on the test. We will try that for sure. Funny thing is, he had verbally told me the 30 watts so I did the math after talking to him on the phone and sent an email to confirm (because it seemed outrageous to me). He sent one email to me which had different numbers on it. He then sent another saying to disregard the first email and then confirmed the use of 8,640 watts. So I don't think it's a typo. What does an applications engineer do? That's who the email was from. He told me he'd been in the solar industry for 25 years.
 
I still say something is wrong.. Just went to Fortress website and found this:

How can a 48 volt 105 amp-hour battery with a 30 watt self draw be 99% efficient? It even says right in the spec sheet there are no fans and self discharge is less than 0.8% per month.

There's an easy way to solve this on your own.. Charge up your batteries and then disconnect one and put it on the shelf.. leave the battery in active mode. Record the voltage every 12 or 24 hours until it goes to the lowest voltage permissible. Then do some simple math.

Really, if that 30 watts is real, not only will you find that the case on the battery is warm to the touch just sitting there doing nothing, but the battery voltage will drop to empty within 7.5 days.. 30 watts x 24hrs = 720 watts x 7.5 days = 5.4kW. That's ridiculous, and I suspect a typo in the email and the guy didn't catch it.
There's one other concern that I have. When we added the 6 additional batteries, we had to have Fortress login to our system and not only update the software but rebalance the batteries which leads me to believe that I can't really rebalance on my own which makes me pretty darn uncomfortable. It's the one issue I'm going to worry about if I take a battery out of the system to run the test you suggest.

We've been up and running now for a few months and show exactly 3 cycles in that time. We've been super careful about trying to prolong battery life and have shut the system down when we felt like the weather wasn't going to be able to get us out of our hole. We do have a generator that we can hook up to recharge but it was only putting in 1% per 12 minutes. We were at 50% at the time so we opted to just put the shop back on the grid until the sun could get us back to full. Today we have that luxury which is nice.
 
Good idea on the test. We will try that for sure. Funny thing is, he had verbally told me the 30 watts so I did the math after talking to him on the phone and sent an email to confirm (because it seemed outrageous to me). He sent one email to me which had different numbers on it. He then sent another saying to disregard the first email and then confirmed the use of 8,640 watts. So I don't think it's a typo. What does an applications engineer do? That's who the email was from. He told me he'd been in the solar industry for 25 years.
An "application engineer" is a fancy term to make an uneducated person feel important in their job. It's a "positive reinforcement" thing.. It makes them feel good about themselves in the hopes they will care about doing a good job.
It means he probably has a high school diploma or maybe even two years of community college. Do not trust any technical information you get from that person. He probably gets 90% correct.. you probably just encountered the other 10%.

In the Air Force, we used to watch training videos and the guy who turned off the classroom lights was called an "Aerospace Illumination Technician".. a joke.
 
ROFL! Thanks for that. I will continue my quest to learn the truth about this overpriced investment that, for 4 months out of the year, will be giving me the one finger salute! I feel like a sucker.
 
There's one other concern that I have. When we added the 6 additional batteries, we had to have Fortress login to our system and not only update the software but rebalance the batteries which leads me to believe that I can't really rebalance on my own which makes me pretty darn uncomfortable. It's the one issue I'm going to worry about if I take a battery out of the system to run the test you suggest.
Well that's damn scary. No way would I let someone into my home network like that..
 
ROFL! Thanks for that. I will continue my quest to learn the truth about this overpriced investment that, for 4 months out of the year, will be giving me the one finger salute! I feel like a sucker.
I don't think you're a sucker.. Fortress seems to have a good reputation and I can't imagine that being the case with them producing batteries that suck 30 watts of power per 5kW module for doing nothing. Like I said, dissipating 30 watts of energy would cause that battery case to get warm just sitting there. It doesn't "add up".

I suspect something else is going on.
 
I don't think you're a sucker.. Fortress seems to have a good reputation and I can't imagine that being the case with them producing batteries that suck 30 watts of power per 5kW module for doing nothing. Like I said, dissipating 30 watts of energy would cause that battery case to get warm just sitting there. It doesn't "add up".

I suspect something else is going on.
Do you think I'd get more answers contacting Northern Arizona Wind & Sun where I bought the equipment? I will say I had one Fortress tech guy refer to my email as being "Quasi emotional" because I said the back and forth emails weren't going to resolve the issue and that I needed a set time for them to work with me as I had a team I was trying to keep on the same page who weren't always here. That particular communication set me off. smh

I struggle to get the help I need because I don't know all the lingo and am not the electrician. My husband was an electrician when he worked but he's had significant memory/cognitive issues this past year so we had to have friends help install the system and I'm the one maintaining it. It's pretty uncomfortable but it makes me an easy person to give the run around to. That's why I posted this on the forum because I smelled a rat but have zero ammo to back it up.
 
Do you think I'd get more answers contacting Northern Arizona Wind & Sun where I bought the equipment? I will say I had one Fortress tech guy refer to my email as being "Quasi emotional" because I said the back and forth emails weren't going to resolve the issue and that I needed a set time for them to work with me as I had a team I was trying to keep on the same page who weren't always here. That particular communication set me off. smh

I struggle to get the help I need because I don't know all the lingo and am not the electrician. My husband was an electrician when he worked but he's had significant memory/cognitive issues this past year so we had to have friends help install the system and I'm the one maintaining it. It's pretty uncomfortable but it makes me an easy person to give the run around to. That's why I posted this on the forum because I smelled a rat but have zero ammo to back it up.

You can give them a try.. and you could also contact Fortress again. Your story is so stunning that I might actually contact them myself as a potential customer, which I am because a friend of mine is interested in an off grid system like mine, only he doesn't want a DIY setup.

I'm an electrical engineer (yeah, a real one lol). So I'll be able to speak to them intelligently on their level and I'll poke the subject of standby draw and see what they have to say.

Just for reference.. a bit of trivia. A Tesla car is said to drain about 1% per day, with actual Tesla owners saying its more like half that much. Doing a bit of math, that means the Tesla uses about 1kW (1000 watts) per day while parked and doing nothing. And that's a whole freaking electric car, not a single battery module.
See how ridiculous that 30 watt quote is? Something's up.. I'm guessing it's 30mW (0.030 Watts).

In the mean time, you need to become more familiar with the antics of your electrons.. and you need to start experimenting to track down that parasitic draw. I would start by going back on grid and isolating the off-grid system completely.. Record the voltage of the battery bank, turn the inverters off, and see what happens. Within 48 hours, you should start getting a good picture of what they're doing. Once you get some bearings on what the batteries do when not powering anything, you can then fire up a single inverter and see what kind of draw it has with a meter.
Do you know how to use a multimeter? If not, you're in for troublesome ride. Unlike grid-tied solar systems, there's really no such thing as a "set it and forget it" off-grid system. To be successful with them, you really need to know your way around. No need to be an engineer or a specialist, but you need to understand what I would describe as "high school level electricity".. Volts, amps, ohms.. watts, watt-hours, etc.
 
I cannot tell you how helpful you've been in such a short conversation! Honestly, THANK YOU! Sadly, I have two electricians and one electrical engineer helping with this system and I seem to know more... How is that even possible? I will learn how to use that multimeter and I will run my experiment with all 10 batteries powering nothing with the inverters off. At least they should stay balanced! ha! I'll start the experiment tomorrow.

In my past life I used to be a Controller (ie, a bean counter/accountant) and I was pretty good at building spreadsheets and analytical tools but I need to understand the parameters I'm calculating. One way I'd set up my spreadsheet is to record the % shown as the SOC on the Sol-Arks just before I shut them off. I could then (24 hours later - or even 12) turn them back on and see what my SOC % was showing on the Sol-Arks and back into the watts used in that 24 hours. That, of course, assumes the SOC is now correct after having work on communication cables with them only a few weeks ago. Does this seem like a valid way to calculate things?

I always like another way to calculate a figure in case I've made some error in my formulas. I'll have to figure out how to find my volts and amps on the software when I hook my computer up to the batteries to get that other figure. Am I right to assume that there should be an amp figure there? I know for sure that voltage is there. I'll start my experiment at 10 in the morning and follow up at 10 at night. And, possibly again Friday morning at 10 just to have the two data points and a full 24 hours.
 
You can give them a try.. and you could also contact Fortress again. Your story is so stunning that I might actually contact them myself as a potential customer, which I am because a friend of mine is interested in an off grid system like mine, only he doesn't want a DIY setup.

I'm an electrical engineer (yeah, a real one lol). So I'll be able to speak to them intelligently on their level and I'll poke the subject of standby draw and see what they have to say.

Just for reference.. a bit of trivia. A Tesla car is said to drain about 1% per day, with actual Tesla owners saying its more like half that much. Doing a bit of math, that means the Tesla uses about 1kW (1000 watts) per day while parked and doing nothing. And that's a whole freaking electric car, not a single battery module.
See how ridiculous that 30 watt quote is? Something's up.. I'm guessing it's 30mW (0.030 Watts).

In the mean time, you need to become more familiar with the antics of your electrons.. and you need to start experimenting to track down that parasitic draw. I would start by going back on grid and isolating the off-grid system completely.. Record the voltage of the battery bank, turn the inverters off, and see what happens. Within 48 hours, you should start getting a good picture of what they're doing. Once you get some bearings on what the batteries do when not powering anything, you can then fire up a single inverter and see what kind of draw it has with a meter.
Do you know how to use a multimeter? If not, you're in for troublesome ride. Unlike grid-tied solar systems, there's really no such thing as a "set it and forget it" off-grid system. To be successful with them, you really need to know your way around. No need to be an engineer or a specialist, but you need to understand what I would describe as "high school level electricity".. Volts, amps, ohms.. watts, watt-hours, etc.
I was just looking at the EG4LL 2.0 and see they have two "Power Consumption" figures on their spec sheets that Fortress never discloses (at least that I can find). And they're nearly the same capacity for half the dang price! I'm feeling rather sick to my stomach at the choices I personally made in putting this system together. I had been watching a lot of Engineer 775 videos and thought these were his normal go-to. If they were before, they don't seem to be now so I'm sure there was a reason.
 
I was just looking at the EG4LL 2.0 and see they have two "Power Consumption" figures on their spec sheets that Fortress never discloses (at least that I can find). And they're nearly the same capacity for half the dang price! I'm feeling rather sick to my stomach at the choices I personally made in putting this system together. I had been watching a lot of Engineer 775 videos and thought these were his normal go-to. If they were before, they don't seem to be now so I'm sure there was a reason.

Relax.. I'm 90% confident the parasitic drain is not in your batteries and that 30 watt figure they gave you was a typo. It makes absolutely no engineering sense. 30 watts per day would be surprising, but reasonable. 30 watts an hour is just nutty unless there are heaters in there.

Also, there is a quality difference between the EG4LL and the Fortress Power with the EG4 being lower on the ladder.

I am in contact with Fortress now, please be patient and don't panic.
 
In my past life I used to be a Controller (ie, a bean counter/accountant) and I was pretty good at building spreadsheets and analytical tools but I need to understand the parameters I'm calculating. One way I'd set up my spreadsheet is to record the % shown as the SOC on the Sol-Arks just before I shut them off. I could then (24 hours later - or even 12) turn them back on and see what my SOC % was showing on the Sol-Arks and back into the watts used in that 24 hours. That, of course, assumes the SOC is now correct after having work on communication cables with them only a few weeks ago. Does this seem like a valid way to calculate things?
SOC is a horrible way to calculate anything beyond "can I make it through the night".. and even then it's a stretch. You want to use actual battery voltage and you need to be able to read it to at least 2 digits like 54.33 volts. (Preferably 3 digits at lower values) General use multimeters on Amazon or your local hardware store are fine for household use or working on a car, but when playing with lithium batteries, you want (need) a quality meter like a Fluke or one of the higher end Klein units. Basically, don't spend less than $100 and preferably about $150.

I always like another way to calculate a figure in case I've made some error in my formulas. I'll have to figure out how to find my volts and amps on the software when I hook my computer up to the batteries to get that other figure. Am I right to assume that there should be an amp figure there? I know for sure that voltage is there. I'll start my experiment at 10 in the morning and follow up at 10 at night. And, possibly again Friday morning at 10 just to have the two data points and a full 24 hours.
Lets go back to square one and diagnose your problem. In the shortest most basic way, describe what your problem actually is. "My batteries are not powering me through the night" or "My batteries are not charging" or "My inverter is shutting down because the batteries are dead".

What is your system doing that makes you think you have a problem?
 
Sol-Ark specs say their idle load is 60 watts so x2 that's 120 watts.

8640 divided by 24 hours = 360 watts per hour = 120 (sol arcs) = 240 watts unaccounted for. That's a lot of power.

As @myles said, do the batteries have heaters? Because that would sure do it.
Specs lie I have found out most lie I have an EG4 spec for 100 watts average idle, measured it is 137 watts.
 
We've been up and running now for a few months and show exactly 3 cycles in that time. We've been super careful about trying to prolong battery life and have shut the system down when we felt like the weather wasn't going to be able to get us out of our hole. We do have a generator that we can hook up to recharge but it was only putting in 1% per 12 minutes. We were at 50% at the time so we opted to just put the shop back on the grid until the sun could get us back to full. Today we have that luxury which is nice.
You need to charge your batteries (if the solar is short) on the grid as running a generator is at least twice as expensive as the grid.
 
Specs lie I have found out most lie I have an EG4 spec for 100 watts average idle, measured it is 137 watts.
Yeah, its like they take clues from the automotive industry fuel economy listings.

I have two Sunny Islands and fortunately for me, their standby and idle current specs are spot on to within 1 watt.
 
SOC is a horrible way to calculate anything beyond "can I make it through the night".. and even then it's a stretch. You want to use actual battery voltage and you need to be able to read it to at least 2 digits like 54.33 volts. (Preferably 3 digits at lower values) General use multimeters on Amazon or your local hardware store are fine for household use or working on a car, but when playing with lithium batteries, you want (need) a quality meter like a Fluke or one of the higher end Klein units. Basically, don't spend less than $100 and preferably about $150.


Lets go back to square one and diagnose your problem. In the shortest most basic way, describe what your problem actually is. "My batteries are not powering me through the night" or "My batteries are not charging" or "My inverter is shutting down because the batteries are dead".

What is your system doing that makes you think you have a problem?
My problem is that without powering anything (ie, no loads), the system has often consumed more power than I uptake in a day and this can continue for several days. I started asking questions on this forum and to Fortress and have received answers from Fortress that, as you've pointed out, make no sense. If my system, as it stands, consumes more power than I uptake then I have nothing left to power critical loads. So my mission has been to first understand what is consuming the power when I have no loads attached and if it truly is the equipment I've purchased that doesn't suit my needs then I am trying to determine if I need to sell and replace the equipment so that I can make it through a winter with at least my water running.

As far as SOC goes, I'm learning it's not accurate. My husband is gone for the weekend so I'm just waiting for his return so he can show me how to use his meters. He has good equipment. I just don't know how to use it. From the BMS software, I am only getting voltage showing 53.5. Each battery shows a different SOC when I look at them in the BMS software. They also show different cycle numbers and pretty big swings in a field labeled "Discharge Energy (kWH)". To me that indicates the system isn't really balancing itself but if I can't trust the SOC, I'm going to have to learn what then to look at from the limited number of fields/data available.
 
My problem is that without powering anything (ie, no loads), the system has often consumed more power than I uptake in a day and this can continue for several days.
When you say "without powering anything, no loads", that leaves a lot open. How do you know there are no loads? Did you physically disconnect the breakers or just assume you didn't have anything running? Even a television that is off will draw power. A battery charger that is plugged in but not charging anything will draw power. Even a desktop computer that is plugged in but turned off will draw power. And that stuff adds up fast.

The only way to be sure no power is being dawn is to either measure it accurately or physically open circuits that feed everything.

I started asking questions on this forum and to Fortress and have received answers from Fortress that, as you've pointed out, make no sense. If my system, as it stands, consumes more power than I uptake then I have nothing left to power critical loads. So my mission has been to first understand what is consuming the power when I have no loads attached and if it truly is the equipment I've purchased that doesn't suit my needs then I am trying to determine if I need to sell and replace the equipment so that I can make it through a winter with at least my water running.
Yup.. and we'll help you figure it out.. My money is on unexpected parasitic loads in the house rather than those batteries.. but we'll get there and figure it out.

As far as SOC goes, I'm learning it's not accurate. My husband is gone for the weekend so I'm just waiting for his return so he can show me how to use his meters. He has good equipment. I just don't know how to use it. From the BMS software, I am only getting voltage showing 53.5. Each battery shows a different SOC when I look at them in the BMS software.
Your batteries are lithium phosphate.. a safe type of lithium. One of the minor drawbacks is that the discharge voltage curve is very flat. It is easy to use a multimeter to determine a full battery from an empty one, but everything in between from about 10% to 90% charge all seems to be within a very small voltage range. For this reason, multimeters don't do a very good job at determining state of charge on phosphate batteries so you kind of have to diagnose their capacity by looking at fully charged and then fully discharged voltages and determining how much juice you sucked from them, or used to charge them, between those two extremes.

They also show different cycle numbers and pretty big swings in a field labeled "Discharge Energy (kWH)".
That is normal. The bigger concern are the individual cell level voltage differences. If your battery has 16 cells in series and the voltage of the highest cell minus the lowest cell is more than a certain amount, then you have issues. Most lithium is kept to within 0.020 volts (20mV) and some folks like to see even less than that. I use lithium ion cells (not as safe but have more power), and I keep mine within 20mV, although during charging they sometimes do get as far out as 50mV.

To me that indicates the system isn't really balancing itself but if I can't trust the SOC, I'm going to have to learn what then to look at from the limited number of fields/data available.
Balancing is about cell level voltages not so much module level.

Still waiting on Fortress to respond.
 
UPDATE: I got a response from Fortress that did indeed claim their BMS uses 30 watts of power. However, this response was from their "application engineer" and as I said, something doesn't add up.. literally.

So he sent me a long email filled with copy and paste information as well as a few of his own statements, what I sent him back was basically what I've posted here about the whopping 30 watts most likely being a misprint or typo. I explained why and requested he verify that specification with one of the engineers who designed the battery. I almost request he verify it with a "real engineer" but backspaced over that and replaced the request with something more diplomatic.

I am again waiting for a reply.. I still say: No way does that BMS draw 30 watts.. even a crappy and cheaply made Chinese BMS doesn't draw 30 watts.
 