Looking for other input from Bluetti users... it is my understanding you CAN NOT bond the Bluetti neutral to the house system. Here is the issue when you are trying to use a transfer switch. There are two different types of transfer switches one for bonded neutrals systems ( this switch transfers both hots and neutral) also for GFCI's
Floating neutral systems do not transfer the neutral and bonds it to the house system.
If you CAN NOT bond the neutral of Bluetti, some furnace systems like Lennox and Boderus will not work. They are looking for their neutral to be bonded thru the system to ground. ( No you can not use a bonding plug they are illegal because they bond the neutral out in the field rather than bond the neutral at the panel, the only place the NEC will allow a neutral to be bonded is at the main disconnect)
Has anyone here bonded the Neutral output of their Bluetti to the house system neutral thru a transfer switch? OR does anyone have any info from Bluetti direct that says it is OK?
Our last contact from them was you can not bond their neutral. Anyone know different?
Just a FYI... Eco flow systems will let you bond their neutral and therefore never have these issues. Thanks in advance!
Floating neutral systems do not transfer the neutral and bonds it to the house system.
If you CAN NOT bond the neutral of Bluetti, some furnace systems like Lennox and Boderus will not work. They are looking for their neutral to be bonded thru the system to ground. ( No you can not use a bonding plug they are illegal because they bond the neutral out in the field rather than bond the neutral at the panel, the only place the NEC will allow a neutral to be bonded is at the main disconnect)
Has anyone here bonded the Neutral output of their Bluetti to the house system neutral thru a transfer switch? OR does anyone have any info from Bluetti direct that says it is OK?
Our last contact from them was you can not bond their neutral. Anyone know different?
Just a FYI... Eco flow systems will let you bond their neutral and therefore never have these issues. Thanks in advance!