For wiring let's talk some numbers.
Let's say you want to run a 100A main panel 200ft between house and container. That would require 3/0 AWG copper or 300KCMIL aluminum for 3% loss.
If you're only 100ft away. That drops to 1AWG Copper or 2/0 Aluminum for 3% or less voltage.
If you're OK running 120V at the inverter but getting 110V in the house you can run numbers for that too. Use this site:
Voltage Drop Calculator | Southwire
www.southwire.com
You need to know the distance of the run and what max load you'll use. As an example we have a 200A main panel, but I've never used more than 9kW at any one moment in time. Meaning I have a 200A panel but never use more than 75A. I have a big panel to accommodate more circuits, not more load.
This is where it gets over my head. The Mrs and I hope to be able to run our house as we also have. With some changes - once we have solar. The change will be to run higher load items ONLY during the sunny days and not at night like before - when Hydro is cheaper. If possible, we would like to be able to provide all the power we need with solar and once we feel comfortable - go off grid and/or sell back. Even if we have to grow into a large system over time with a second array at some point.