Since the inverter is 3000w the math would say 3000w ÷ 48v = 62.5amps. But I would imagine you have a common port BMS so charger and inverter will use the same wire. And the charger is 80amps. So the 100amp fuse will be fine.
 
Since the inverter is 3000w the math would say 3000w ÷ 48v = 62.5amps. But I would imagine you have a common port BMS so charger and inverter will use the same wire. And the charger is 80amps. So the 100amp fuse will be fine.
That's what I was thinking just to keep a fire from starting seems like been number of threads here with inverters catching fire after something shorts out want to keep the fuse as close to max power as I can.
 