Not wanting to hijack another members thread, I am experiencing something very peculiar with the 3000w inverter. System is completely off grid.
With no wires connected to any of the ac terminals, I get a reading of 71vac on the N-G ac out, and and 49vac on L-G ac out. L-N is 119vac.
And voltage carries to the ac input N and G terminals to about 63vac.
This can't be correct right?
If bonding and working properly, N-G should be near 0.
Signature Solar has emailed me saying it is normal and a non issue, but it causes phantom voltage to make lights not turn all the way off and weird surges.
With no wires connected to any of the ac terminals, I get a reading of 71vac on the N-G ac out, and and 49vac on L-G ac out. L-N is 119vac.
And voltage carries to the ac input N and G terminals to about 63vac.
This can't be correct right?
If bonding and working properly, N-G should be near 0.
Signature Solar has emailed me saying it is normal and a non issue, but it causes phantom voltage to make lights not turn all the way off and weird surges.