1. I don't connect AC ground to AC output...only AC input..correct?
2. For 6500ex's shipped after Feb 2023, the n-g screw is removed...just to confirm.
3. I will be running two 6500ex split phase. My main panel has N-G bonded and is fed by utility, 6500ex will be fed after the main with AC, I'm a little confused if I need a certain firmware update or setting adjustment regarding the n-g bypass or ? I keep getting lost in the n-g bond eg4 video.
4. Is it best to have the batt bank switched off at two breakers first, and power the AIO's first with PV, so I can set them up as split phase (master one/slave other) and eg4 battery setting and SBU setting?
5. If so, I guess after this I turn off the PV, then switch the batt bank breakers on following eg4 startup procedure, then on batt's one at a time, then turn inverters on.
6. Do I need to check the voltages of the lifepower4's beforehand and charge them up somehow, to get them charged within .1v of each other before doing the above procedure...I have a couple batts that have sat for months but still have 3 SOC lights showing?
2. For 6500ex's shipped after Feb 2023, the n-g screw is removed...just to confirm.
3. I will be running two 6500ex split phase. My main panel has N-G bonded and is fed by utility, 6500ex will be fed after the main with AC, I'm a little confused if I need a certain firmware update or setting adjustment regarding the n-g bypass or ? I keep getting lost in the n-g bond eg4 video.
4. Is it best to have the batt bank switched off at two breakers first, and power the AIO's first with PV, so I can set them up as split phase (master one/slave other) and eg4 battery setting and SBU setting?
5. If so, I guess after this I turn off the PV, then switch the batt bank breakers on following eg4 startup procedure, then on batt's one at a time, then turn inverters on.
6. Do I need to check the voltages of the lifepower4's beforehand and charge them up somehow, to get them charged within .1v of each other before doing the above procedure...I have a couple batts that have sat for months but still have 3 SOC lights showing?