Main failure mode for mosfets and diodes is short-circuit. You also want to protect against accidental short-circuit by operator error.
Are you saying the internal fuse won’t protect this situation?
Main failure mode for mosfets and diodes is short-circuit. You also want to protect against accidental short-circuit by operator error.
This whole discussion is based on the assumption that the inverter will destroy itself trying to put out more power than it can safely do.
Is there any evidence that this is true?
To the contrary, any inverter I have used has an internal fuse which is happy to sacrifice itself in this case.
Over current protection (fuse) for battery and External Charger circuits has NOT been provided and has to provided by the installer / user. See guidelines at Tables 1.3(a) and 1.3(b) for recommended sizes for installation in free air and conduit respectively. National and Local Electrical Codes will supersede these guidelines.
The inverters are fitted with an internal DC fuse (see table above for rating). If the DC cable length is increased to more than 1,5m, an additional fuse or DC circuit breaker must be inserted close to the battery.Reverse polarity connection of the battery wires will blow the internal fuse and can damage the inverter. The internal fuse is not always replaceble (see table above).
A wrench across the terminals was an example of a "dead short", just as a short in your main cable running from the battery would be.If I drop a wrench across the terminals unless the fuse is the terminal how is a fuse gonna help. Please I'm not trying to be argumentative. I just think I want my fuses protecting my devices and by default the wires will be protected.
Trust me I know from much experience the utility of fuses. Every time I trip a breaker I say WOW glad I had that there.
2+ years ago I bought a Bestek 300W pure sine wave inverter that had a bunch of good reviews at the time. It's been sitting in it's box ever since. Yes I know, I'm the dumb guy, who should have plugged it in when I first got it. Last week I cut the cig plug off the end and wired a Anderson Power Pole on it. I checked the polarity multiple times to be sure I had it correct. Took it out and plugged into my new battery build. Heard a large POP and smelled burnt electronics. I wired a Anderson Power Pole on the cig plug and checked it plugged in to my car and I did have the polarity right. Now I have $50 of junk. On this particlur inverter there was no fuse, either in the cig plug or the inverter.A valid question, the assumption is based on the video (the link takes you to the relevant part of the video) I linked to from Pacific Yacht Systems / Jeff Cote, where he explicitly states that inverters will exceed their ratings if asked to.
...snip....
That said, it seems logical that inverter manufacturers (at least top tier ones) would fuse the devices internally, maybe some do, I don't know, consult your manual, but based on the video I get the impression that most do not.
I just took a quick peak at a few inverter manuals.
...snip.....
2+ years ago I bought a Bestek 300W pure sine wave inverter that had a bunch of good reviews at the time. It's been sitting in it's box ever since. Yes I know, I'm the dumb guy, who should have plugged it in when I first got it. Last week I cut the cig plug off the end and wired a Anderson Power Pole on it. I checked the polarity multiple times to be sure I had it correct. Took it out and plugged into my new battery build. Heard a large POP and smelled burnt electronics. I wired a Anderson Power Pole on the cig plug and checked it plugged in to my car and I did have the polarity right. Now I have $50 of junk. On this particlur inverter there was no fuse, either in the cig plug or the inverter.
IIRC most Cig sockets are fused @20A, and a 300W inverter can't pull all 300W from one without popping the fuse. That's why they sell a battery clamps to cig plug adapter that is unfused to use with them.Well that's one data point but I think it may not be representative.
A typical cig socket is probably fused at ~12.5 amps.
I had a really cheap inverter from a company that I will not even name to protect the guilty.
Rated for 500 watts actually capable of ~300 watts and it was fused.
If you have seen any of the David Poz YT videos he routinely tries to overload inverters and they usually protect themselves.
The point I want to make is that the generally accepted wisdom is true:
A proper fuse is present to protect the wire.
A properly designed device protects itself. Period.
I don’t think it makes sense to underrate your wire protection fuse in hopes of adding device protection. Makes no sense to me.
And if the simple purpose of “protecting the wire” isn’t sexy enough then in your mind change that phrase to “protecting the wire from a catastrophic failure that burns down my house and kills me while I sleep”. ?
I'm not sure if this is directed at me
I try to remember that these posts live on forever and merely want to reinforce that protecting the wire is a noble cause.
I stand by what I said and really don’t have anything else to add.
If a device is poorly designed I will be sure to blow it up early and never look back once the smoke clears. The rest of my system will be properly protected.
Another thing about a circuit breaker at the inverter end. A properly constructed DC circuit breaker has a way of dealing with a internal spark. Using the circuit breaker as a switch, should take care of the spark you get when connecting a inverter to it's power source.In that case we are definitely in agreement on that point.
Fair enough, I think I pretty much understand your perspective and see where you are coming from. I think I just have a somewhat more cautious philosophy and feel that the cost/benefit of adding a breaker to protect the inverter costs almost nothing (in dollars and in watts) relative to the cost of a replacing a moderately expensive inverter. Even if the device is internally fused, resetting a breaker is much more convenient than replacing an internal fuse. This is just my 2 pence, as I said above, I often err on the side of caution and 'over engineer' things..
edit: and obviously its reasonable that the amount of caution should be somewhat proportional to the cost of the inverter. Destroying or wearing out a couple $100 dollar inverters is a lot different than damaging a $1500 dollar inverter/charger
I have also noticed with my SSR's there is no spark either.Another thing about a circuit breaker at the inverter end. A properly constructed DC circuit breaker has a way of dealing with a internal spark. Using the circuit breaker as a switch, should take care of the spark you get when connecting a inverter to it's power source.
At least I think it would, if wrong please point out where I am.
- A breaker (dual pole? single pole?) between the Solar panel and the charge controller. For reasons discussed on page 1 of this thread and in this blog post, overcurrent protection might be impractical and unneccessary at this leg of the charging circuit, but being able to isolate the system from the charge source is useful.
A lot (most?) of the SCCs have built in over-current protection. However, if it doesn't then Yes, a properly sized fuse at the SCC is needed in order to keep things safe.
- A fuse or breaker close to the SCC sized for the wire between the battery and the SCC. In the event of a short between the battery and the SCC this would stop current flowing from the SCC.
- A fuse or breaker close to the Battery side of this circuit, sized for the wire between the battery and the SCC. In the event of a short between the battery and the SCC this would stop current flowing from the battery.
I suspect that I might be misunderstanding how current would behave in the event of a short between the battery and SCC. If the positive wire got severed and shorted to ground (lets say the chassis of a vehicle), would that create two energized circuits (one energized by the battery and the other by the charge controller/pv panel?
A lot of the Charge controllers have built-in over-current protection. In this case, just the fuse at the battery should be sufficient. If there isn't built in protection then yes, a properly sized fuse would need to be placed on the output of the charge controller.