I'd prefer as an SDS. The problem is the firmware updates for mobile don't work for the flickering lights or the MPPT lock at 90V PV input.So, some time has passed, and I think some of you are changing your setting for the common neutral.
this includes MPP LV6548.
Any thoughts?
What about the preference for a SDS and being able to service the inverters?Absolutely, common neutral.
Anything else is an exception to normal.
Unless the system is mobile. Then dynamic bonding is required.
A SDS just adds complications.What about the preference for a SDS and being able to service the inverters?
Current on neutral?A SDS just adds complications.
And I don't see how it would create any problems with servicing.
Nothing wrong with adding a 3PDT in a common neutral system for service or bypass of the inverters.What about the preference for a SDS and being able to service the inverters?
Ever touch a neutral that is open and has current?Current on neutral?
Shouldn't be any current on neutral when AIO is off. (If installed correctly)Current on neutral?
I have became part of the return path more times than I care to admit. But the worst one was a loaded 277v lighting neutral. That one almost ended it all.Ever touch a neutral that is open and has current?
I have, certainly tingles the senses.